new wiring construction

This is my set up I am using for a portable building 10x 12 inside dimensions

breaker panel on outside pole 30 amp
wire from breaker pole to inside breaker panel 10/3

inside breaker panel 2 breakers 20 amps

circuit 1 1 15 amp outlet
circuit 2 1 15 amp outlet 1 light fixture (Ceiling fan)

Heaviest load will be on circuit 1 as that will be used for a 5k btu ac window unit.

Question:
Will the 30 amp breaker on the outside pole be sufficient or do I need to run a 40 amp breaker.

I know I could have used 12 gauge wire on the outside line but I wanted to future proof the outside feeder if I ever needed more power.

and yes I probably over engineered this set up.
 
Sponsored Links
  #2  
Old 07-03-12, 08:10 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,677
You could not have used #12 on a 30 amp breaker. Your plan sounds fine and you have capacity for more branch circuits in the subpanel. Just be sure to add an eight foot ground rod, a bonded ground bar and isolate the neutral bar.
 
  #3  
Old 07-03-12, 08:45 AM
SeaOn's Avatar
Member
Join Date: Dec 2011
Location: USA
Posts: 351
I agree with ray
 
  #4  
Old 07-03-12, 04:41 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,221
breaker panel on outside pole 30 amp
wire from breaker pole to inside breaker panel 10/3
What type of cable are you using to feed the panel in the building? If this is SO, SOW, SJ or similar type cable you should have used 10-4
 
  #5  
Old 07-03-12, 06:05 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
breaker panel on outside pole 30 amp
wire from breaker pole to inside breaker panel 10/3
Is this a 120 or 120/240 circuit? If it's 120/240, you need 10/4.
 
  #6  
Old 07-03-12, 06:12 PM
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 4,064
...inside breaker panel 2 breakers 20 amps
Using 12ga wire no doubt. Just making sure...
 
  #7  
Old 07-03-12, 06:34 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,365
Flexible cords like SO, SJO, SOOW and the like cannot be used in place of permanent wiring.
 
  #8  
Old 07-03-12, 06:45 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
Flexible cords like SO, SJO, SOOW and the like cannot be used in place of permanent wiring.
This is a portable building, he has to use this.
 
  #9  
Old 07-04-12, 07:07 AM
Member
Thread Starter
Join Date: Jul 2012
Posts: 2
will the ground wire and set up circuit on the outside breaker box be sufficient for grounding or do I need to run a second ground bar there is only a total of 25 ft distance (Wire length not straight line distance) from point to point between the two breaker boxes.

When I buried the conduit I placed bricks over the top. I figure if they can't guess from the two ends of plastic conduit and the bricks there is a wire in the ground I want to sit back and watch the fireworks with a beer in my hand laughing when they dig it up.

I ran 12-2 wire on the inside. This particular building will never be upgraded. IF it is I will have to install a larger box as I only have a 2 breaker panel box inside It is for a small retail shop. the future proofing is in case I ever end up moving the building from the property and they put another building in.
 
  #10  
Old 07-04-12, 07:31 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,677
How deep is the conduit" What kind of wire did you run? THWN?

or do I need to run a second ground bar there is only a total of 25 ft distance (Wire length not straight line distance)
Wire length is not a factor. The subpanel must have an isolated neutral bar and a bonded ground bar. Since ground bars are not usually included you would probably need one. In addition you need a ground rod driven eight feet in the ground. Both the EGC* from the main panel and the GEC* from the ground rod go to the ground bar. The GEC can be as small as #8 but if you make it #6 it will not need to be in conduit.

*Definitions
EGC= Equipment grounding conductor, the green or bare wire from the pole panel.
GEC= Grounding electrode conductor, the wire from your ground rod
 

Last edited by ray2047; 07-05-12 at 05:32 PM.
  #11  
Old 07-04-12, 11:06 AM
SeaOn's Avatar
Member
Join Date: Dec 2011
Location: USA
Posts: 351
The GEC can be as small as #10 but if you make it #6
The minimum size a GEC can be is a #8.
 
  #12  
Old 07-05-12, 04:12 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,221
Both the EGC* from the main panel and the GEC* from the ground rod go to the neutral bar.
Ummm...Ray, I think you meant ground bar.
 
  #13  
Old 07-05-12, 04:26 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,365
CJ, thanks for the catch. I changed Rays post.
 