6 wall plugs no voltage
#1
Member
Thread Starter
Join Date: Jul 2012
Posts: 14
Upvotes: 0
Received 0 Upvotes
on
0 Posts
6 wall plugs no voltage
I measure 118 volts from hot to ground 118 volts neutral to ground 0 volts hot to neutral. any thoughts. My wife was blow drying her hair when all went south. I've removed the gfci that i thought blew, but still nothing.
#2
Did you turn the breaker all the way off then on? Are all of the receptacles on the load side of the GFCI? (They probably shouldn't be unless they are all in a bath, kitchen or unfinished basement.) Have you checked all of the connections and moved any back stabs to the screws?
Please tell us how you measured that.
118 volts neutral to ground
#3
Welcome to the forums!
In addition to Ray's questions, have you read Troubleshooting a dead receptacle or light + Basic Terminology? It's one of the sticky posts at the top of the forum page.
I've removed the gfci that i thought blew, but still nothing.
#4
Member
Thread Starter
Join Date: Jul 2012
Posts: 14
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I've check the connections all seem to be ok. i went ahead and removed and reinstalled the plugs to make sure the connections were good. I don't know what a backstab is. Could you explain please? I thought it was just a bad gfci but with it removed and a standard receptacle replacing it nothing works.
#6
Member
Thread Starter
Join Date: Jul 2012
Posts: 14
Upvotes: 0
Received 0 Upvotes
on
0 Posts
My apologies I've just read the primer in terms and yes I did change two receptacles to the proper wiring (no backstab). now what should i check. I notice that this circuit has more plugs. I've reconnected the wires. Still reading the same.
#7
Group Moderator
Typically, when some of the receptacles on a circuit work and some do not, the problem is at the last good one or the first bad one.
#10
I measured by touching the voltmeter lead (set at 200 VAC) to the white wire and the other lead to the ground wire. Is that correct?
Read more: http://www.doityourself.com/forum/ne...#ixzz1zryUHIdJ
Read more: http://www.doityourself.com/forum/ne...#ixzz1zryUHIdJ

#11
Would a loose neutral cause every plug to read the same.
Also please answer the questions I previously asked.
Are all of the receptacles on the load side of the GFCI? (They probably shouldn't be unless they are all in a bath, kitchen or unfinished basement.)
Have you checked all of the connections and moved any back stabs to the screws?
Please tell us how you measured that.
Have you checked all of the connections and moved any back stabs to the screws?
118 volts neutral to ground
#12
Member
Thread Starter
Join Date: Jul 2012
Posts: 14
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I've replaced the breaker, still the same. Should I be reading the 118 volts on both the hot and neutral sides when going to ground? And why do I read 0 volts from hot to neutral
#14
NO, you have incoming power that must be attached to the LINE side. You need to determine which cable is incoming, attach them to the LINE side, and the remainder to the LOAD side.
#15
You need to determine which cable is incoming, attach them to the LINE side, and the remainder to the LOAD side.
#16
Would a loose neutral cause every plug to read the same.
Should I be reading the 118 volts on both the hot and neutral sides when going to ground? And why do I read 0 volts from hot to neutral
And as Mitch said,
Typically, when some of the receptacles on a circuit work and some do not, the problem is at the last good one or the first bad one.
#17
I notice that this circuit has more plugs.
now what should i check.
#18
Member
Thread Starter
Join Date: Jul 2012
Posts: 14
Upvotes: 0
Received 0 Upvotes
on
0 Posts
trying to answer all the questions
The GFCI is now out of the circuit. There are a total of 6 wall outlets in the circuit, 3 in the bathroom (hence the GFCI) and 3 in my living room . with all kinds of electronics hooked up. Or at least the electronics was hook up . It is now plugged into another circuit. And it seem that a light switch is also in the circuit??? I thought lights and wall plugs were supposed to be on different circuits. AS far as the first load on the circuit I don't know how to tell since the light switch and 3 receptacles are in the same room on the same wall. And the breaker is 20 amp
#19
Thanks, Nash, I forgot about lighting, etc. that may not need protection.
Dwind, are there ANY receptacles on that circuit that work?? If so, find one, measure it's voltage from hot to neutral. If it is normal, move right or left to the next one. Either the wiring from that last working receptacle is compromised, or the wiring to the first one that is not working is compromised. I said it in a longer fashion than the others, but basically that is the way to trouble shoot it.
Dwind, are there ANY receptacles on that circuit that work?? If so, find one, measure it's voltage from hot to neutral. If it is normal, move right or left to the next one. Either the wiring from that last working receptacle is compromised, or the wiring to the first one that is not working is compromised. I said it in a longer fashion than the others, but basically that is the way to trouble shoot it.
#21
The normal reading would be 120 hot to ground and hot to neutral. Neutral to ground should read zero or almost zero.
Your reading of 120 to ground but nothing from hot to neutral tells us you have a failed neutral connection.
Your reading of 120 to ground but nothing from hot to neutral tells us you have a failed neutral connection.
#25
When you changed your breaker, did you check the neutral connection on the buss bar? If absolutely NO receptacles on this circuit have any voltage, then you gotta go back to the origin, which is the breaker panel. We can help if we know all the information. You must answer the questions. Do any of your lights work that are on this circuit?
One more thought...do you have any receptacles on the outside of the house that may be serviced by this breaker?
One more thought...do you have any receptacles on the outside of the house that may be serviced by this breaker?
#26
Member
Thread Starter
Join Date: Jul 2012
Posts: 14
Upvotes: 0
Received 0 Upvotes
on
0 Posts
i just found a plug in my bedroom that ic controlled by this circuit and IT IS WORKING. Ok so if the plug is working is the problem between it and the next plug?i've put a circuit tester (3prong ) in the first outlet . It reads open neutral and hot/grnd reverse. Here is the catch when i flip the light switch the hot/ground reverse light goes out. What the heck? The switch controls 2 can lights
#27
when i flip the light switch the hot/ground reverse light goes out.
i've put a circuit tester (3prong ) in the first outlet .
#28
i just found a plug in my bedroom that ic controlled by this circuit and IT IS WORKING. Ok so if the plug is working is the problem between it and the next plug?
I'm also guessing that you may have just found the box where the power feed from the panel first connects to the outlets it is supplying. For that reason alone, I would kill the power, pull the working receptacle, and make sure everything there is as it should be.
Note: Now you have a starting point to follow the process Chandler described in post #19.
Note 2: The suggestions Ray and Chandler have just posted are also excellent advice.
#29
Member
Thread Starter
Join Date: Jul 2012
Posts: 14
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Because I found this problem and saw that the wiring coming into the two different items(switch and receptacle) I figured there must be a hidden junction. I opened the wall and low an behold a j box with the hot neutral and ground. I took them apart and found a scorched wire. I was able to cut out the bad area and reattached one set of wires at a time and checked them with the circuit tester. All is well. Now I've got a jbox cover on the wall instead of in the wall. Hopefully this is the end of my problems. I've instructed the wife to use a different receptacle(diff Circuit) for her hair dryer. Now I need to figure out how to divide up all the electronics to different circuits. Since I just took apart and put the joints back together, do you think it was just a loose neutral?
Thanks to all of you.
P.S. Is there anything I forgot?
Thanks to all of you.
P.S. Is there anything I forgot?
#31
Cahndler did not help.
and IT IS WORKING
As Ray said, that's a great repair and detective work you did. Glad you got it fixed. Sometimes we have to badger for information. Sorry it took so long.
#33
Because I found this problem and saw that the wiring coming into the two different items(switch and receptacle) I figured there must be a hidden junction.