Microwave trips breaker
#1
Member
Thread Starter
Join Date: Jul 2012
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Microwave trips breaker
Everytime I use my microwave the lights go out and I have to reset one of the breakers in the box. Can someone tell me if this is a problem with the microwave or a problem with the breaker panel or a problem with the wiring in my house? If it's as simple as replacing the microwave then I'd rather do that than spending a lot of money on an electrician. I'd like to have some idea as to what I'm dealing with so if I do have to call an electrician I won't be given false or inaccurate information.
Thanks
Mink
Thanks
Mink
#2
So what else is on the circuit? Is it a 15 amp or 20 amp breaker? Have you tried it on a different circuit?
If this is in a kitchen it should be plugged into one of the 20a counter top receptacles. There should be no lights on those circuits.
Above assumes a counter top microwave not a built in.
Everytime I use my microwave the lights go out
Above assumes a counter top microwave not a built in.
#3
A built-in microwave should be on a dedicated circuit. I suspect yours is wired where a kitchen exhaust hood was. These are typically on a lighting circuit.
#4
Member
Thread Starter
Join Date: Jul 2012
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The microwave is a built in, not a countertop model (it's built into the wall), the stove is on the other side of the kitchen. Do you think I will run into the same problems if I just replace the microwave with a regular countertop model and putt on a shelf in that space in the wall?
#5
Do you think I will run into the same problems if I just replace the microwave with a regular countertop model and putt on a shelf in that space in the wall?
Is this a new install or has it been working up till now without tripping the breaker. If it is a new install you need to get who ever installed it out to correct his mistake. If it is an old install that just started doing this it could be something new added to the circuit, a bad breaker, or a fault with the microwave.
#6
Member
Thread Starter
Join Date: Jul 2012
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I don't know anything about circuits or what else is on it...I don't even know how to check to see what's on the circuit, I have no knowledge of this stuff, I'm a single female who bought this house 6 months ago, the problem has been happening since I bought the house....and the microwave is not new, I can tell it's a very old style....so I'm fairly certain this wasn't recently installed. There's an outlet in the kitchen also that if I plug something in to that (coffee maker or toaster, etc.) and use the microwave it also trips the breaker.
#7
Bottom line the kitchen probably needs rewiring. We can help you do it yourself if you want. I would suggest you buy the book Wiring Simplified available at Home Depot, Amazon, and other places so you know the basics.
#9
There should be a dataplate on the microwave that tells how many watts the oven draws. If you can post that more info can be given.
#10
In addition,
Knowing both the power requirements of the microwave and the power available on the circuit may help us give you better advice.
The rating of the circuit breaker should be clearly stamped into its handle.
Is it a 15 amp or 20 amp breaker? (from post #2
The rating of the circuit breaker should be clearly stamped into its handle.
#11
Member
Thread Starter
Join Date: Jul 2012
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Your Opinions Please ???
OK, so I had two electricians come in and assess the problem witht he microwave in my basement and they determined that everything in the kitchen is on one 15 amp breaker (the microwave, dishwasher, fridge, stove, all outlets, lights, pot lights). They told me that each of those major applicances would need to be on it's own separate line. They said there is no more space in the breaker box, so one of them said they'd have to put in a subpanel, the other guy said no that's not the way to go that he could split the breakers to make two out of one. I don't know who's right and who's wrong and which is the best way to go.
Also, someone told me that because my house is only 100 amps that I really should have it upgraded to 200 amps....
Because I am not knowledgeable in any of this stuff I really want some ideas on what I should do to resolve this problem and not risk running into other electrical problems later on.
The house is a raised bungalow. There is a kitchen and washroom on the main floor and a finished basement apartment, two people in all living in the house, me living alone on the main floor and a tenant living in the basement. Someone said that because this is technically considered a two family home then 200 amp service is necessary....any advice or responses to that???
The prices they're quoting me to do this stuff is much higher than I had expected, 3000.00 to put the microwave, dishwasher, fridge and stove on their own separate lines, and 6000.00 if I want to upgrade to 200 amp service. Does this sound reasonable or is it outrageous? I'm in the Toronto (Canada) area.
I'm so frustrated with this, as I don't have the knowledge to make educated choices and the people here on this forum is the only soucre of non-biased info I have.
Would really appreciate everyone's thoughts and opinions and advice on this...
Thanks
Maxine
Also, someone told me that because my house is only 100 amps that I really should have it upgraded to 200 amps....
Because I am not knowledgeable in any of this stuff I really want some ideas on what I should do to resolve this problem and not risk running into other electrical problems later on.
The house is a raised bungalow. There is a kitchen and washroom on the main floor and a finished basement apartment, two people in all living in the house, me living alone on the main floor and a tenant living in the basement. Someone said that because this is technically considered a two family home then 200 amp service is necessary....any advice or responses to that???
The prices they're quoting me to do this stuff is much higher than I had expected, 3000.00 to put the microwave, dishwasher, fridge and stove on their own separate lines, and 6000.00 if I want to upgrade to 200 amp service. Does this sound reasonable or is it outrageous? I'm in the Toronto (Canada) area.
I'm so frustrated with this, as I don't have the knowledge to make educated choices and the people here on this forum is the only soucre of non-biased info I have.
Would really appreciate everyone's thoughts and opinions and advice on this...
Thanks
Maxine
#12
Half breakers can be used if your panel is approved for that and is the cheaper solution. However given the number of circuits a subpanel might be a more desirable solution. We can help you do either of these two things yourself for a few hundred dollars as stated earlier.
Last edited by ray2047; 07-26-12 at 10:58 AM.
#13
someone told me that because my house is only 100 amps that I really should have it upgraded to 200 amps...
Someone said that because this is technically considered a two family home then 200 amp service is necessary...
Upgrading the service is not a DIY job. As Ray suggested, we can help you safely install a subpanel or exchange some full size breakers for tandem breakers to add more circuits in your existing panel. A subpanel, in addition to allowing you to add a larger number of circuits, might also allow you to separate the apartment loads from the main floor or main floor loads, depending on how the branch circuits are run.
We may be giving you a lot of information to absorb. Please post back with any questions, including any requests for clarity.