PapaSmoke: New Electric Breaker box installed - now WELL is FUNKY
#1
Member
Thread Starter
Join Date: Jul 2012
Posts: 8
Upvotes: 0
Received 0 Upvotes
on
0 Posts

I recently had a new breaker load center installed. Since that day, my well runs continuously. I checked the pressure switch and it APPEARS to close at 40PSI and open at 60PSI but the well pump continues to run. Pressure in the bladder tank RAPIDLY builds to 100+PSI. I took the cover off the pressure switch and it APPEARS to be open but the pump still runs.
Thoughts? Tips? Help needed SOON as I don't like manually switching the breaker on whenever I need water.
Can this be caused by the electrician having wired the load center incorrectly?
Mod Note: Post moved from Pumps and Wells.
Thoughts? Tips? Help needed SOON as I don't like manually switching the breaker on whenever I need water.
Can this be caused by the electrician having wired the load center incorrectly?
Mod Note: Post moved from Pumps and Wells.
Last edited by ray2047; 07-21-12 at 12:30 PM.
#3
Member
Thread Starter
Join Date: Jul 2012
Posts: 8
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The pump is submersible.
The ONLY changes made were the electrician removed the old breakers and installed new breakers. The well pump worked fine until the electrical changes were made.
The ONLY changes made were the electrician removed the old breakers and installed new breakers. The well pump worked fine until the electrical changes were made.
#5
Member
Thread Starter
Join Date: Jul 2012
Posts: 8
Upvotes: 0
Received 0 Upvotes
on
0 Posts
This is very strange. I have the power off ALWAYS since I don't want the pump running. I checked the switch. Closed at 40 - open at 60. Pump runs ALWAYS. I killed power again. I cut two small plastic inserts and put them between the contacts so they MUST remain open. Powered on. Pump ran from 35 to 70 pounds, when I shut it off. At 40, the switch closed. At 60, it opened.
NOW you see why I am so puzzled and suspect the electrician did something wrong. Do you think there could be a short in the breaker or something along that line?
BTW - THANK you for your time and help, lawrosa. If this wasn't driving me crazy, I would be having fun doing this!
NOW you see why I am so puzzled and suspect the electrician did something wrong. Do you think there could be a short in the breaker or something along that line?
BTW - THANK you for your time and help, lawrosa. If this wasn't driving me crazy, I would be having fun doing this!
#6
I am not sure the wiring in regards to the series of events but the pressure switch wiring to/in the relay box must be installed incorrectly. I am pressty sure the presure switch just trips the relay to turn the pump on. So in the box you should note that regardless what the pressure switch is doing the relay is always closed.
Can you give a make and model of the relay box?
Secondly, you paid for a service and it is wrong. You probably should not mess with it and absolutely call the electrician back. He should cover his fault at no charge to you.
Thats the best advice I could give you.
Can you give a make and model of the relay box?
Secondly, you paid for a service and it is wrong. You probably should not mess with it and absolutely call the electrician back. He should cover his fault at no charge to you.
Thats the best advice I could give you.
#8
Member
Thread Starter
Join Date: Jul 2012
Posts: 8
Upvotes: 0
Received 0 Upvotes
on
0 Posts
MAYBE...in the breaker? NOTHING has changed as far as the pressure switch goes and the well goes. I REMOVED the white and black wires from the pressure switch. The pump STILL runs (WTH!!???). Also, I am reading nearly 400V!! This is really freaking me out now!
#9
Member
Thread Starter
Join Date: Jul 2012
Posts: 8
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ready for this? I CALLED him. He LOUDLY denies being at fault and says "You have power to the pump so I did MY part of the job right. I don't mess with wells. If you could change out the pressure switch, I will come out to look at it."
I reminded him everything worked GREAT before he changed the breakers and NEVER worked properly after that. The 400V I am reading gives me great concern and tells me he did something wrong.
I removed the wires and tested voltage. That is as good as he gets.
I WILL let you know what transpires....
I reminded him everything worked GREAT before he changed the breakers and NEVER worked properly after that. The 400V I am reading gives me great concern and tells me he did something wrong.
I removed the wires and tested voltage. That is as good as he gets.
I WILL let you know what transpires....
#10
Well (bad choice of words?)....you can't be getting 400V if your supply is only 240. Either you have the meter set wrong...or it's a digital picking up weird stuff.
#13
Member
Join Date: Jan 2008
Location: Southeastern Pennsylvania
Posts: 3,313
Received 116 Upvotes
on
107 Posts
Hey Papa I’m not an expert on electric or plumbing but I have well with pressure switch and motor control box on basement wall. Is it possible that there are 2 circuits in the panel on two breakers? One bypasses the pressure switch and goes right to the terminals in the control box for the pump. The other goes to the pressure switch first.
Was just thinking maybe someone had setup a scheme whereby if the pressure switch or anything else before the control box wasn’t working properly, they could then turn that breaker off and throw the other breaker on, and thus be able to run the pump directly from the panel for a short time, get some water then turn the breaker off. In other words it would be an emergency bypass circuit.
You get a guy in who just innocently replaces all the breakers and turns them all on and all hell breaks loose with respect to the pump. Crazy voltages, non-stop pumping, etc.?
But I see flaws in this picture:
(1) I know so little about electric circuits maybe that scheme is totally impossible.
(2) It assumes you would not have ever noticed you had a breaker that was never turned on.
Good luck! What a mystery.
Was just thinking maybe someone had setup a scheme whereby if the pressure switch or anything else before the control box wasn’t working properly, they could then turn that breaker off and throw the other breaker on, and thus be able to run the pump directly from the panel for a short time, get some water then turn the breaker off. In other words it would be an emergency bypass circuit.
You get a guy in who just innocently replaces all the breakers and turns them all on and all hell breaks loose with respect to the pump. Crazy voltages, non-stop pumping, etc.?
But I see flaws in this picture:
(1) I know so little about electric circuits maybe that scheme is totally impossible.
(2) It assumes you would not have ever noticed you had a breaker that was never turned on.
Good luck! What a mystery.
#15
Member
Thread Starter
Join Date: Jul 2012
Posts: 8
Upvotes: 0
Received 0 Upvotes
on
0 Posts
ZOESDAD! I suggested this to my electrician when he showed up. Guess what!?? That is EXACTLY what somebody did back in 1973! My guy called it a "cold wire" connection or something like that. I showed him how the pump still ran with the wires to the switch disconnected. He said the same thing I said - "WHAT THE HELL!? That is impossible!" 
He suddenly began to stare into space - looked like a deer in my headlights - and then - ***WHAM!!!*** ""I got it!" He ripped the cover off my load center and started pulling breakers. In 5 minutes, it was fixed. Life DOES have sweet moments!
I asked about the 400 volts. He tried my volt ohm meter. He tossed it into the can. I asked, "So I can finally buy the digital model my wife told me I could not have?". Redeeming himself for not catching the unusual wiring, he said, "YEP!"
BTW - he fixed it the RIGHT way! Boy, does my water taste GREAT!
THANKS ALL! This case is closed!

He suddenly began to stare into space - looked like a deer in my headlights - and then - ***WHAM!!!*** ""I got it!" He ripped the cover off my load center and started pulling breakers. In 5 minutes, it was fixed. Life DOES have sweet moments!
I asked about the 400 volts. He tried my volt ohm meter. He tossed it into the can. I asked, "So I can finally buy the digital model my wife told me I could not have?". Redeeming himself for not catching the unusual wiring, he said, "YEP!"
BTW - he fixed it the RIGHT way! Boy, does my water taste GREAT!
THANKS ALL! This case is closed!
#16
Glad you got it. Thanks to Zoesdad for helping out.
An analog meter is actually better then a digital unless the digital is a more expensive brand name. The lower impedance of even a cheap analog meter helps prevent false readings caused by induced voltages.
An analog meter is actually better then a digital unless the digital is a more expensive brand name. The lower impedance of even a cheap analog meter helps prevent false readings caused by induced voltages.
#17
THANKS ALL! This case is closed!
Tech note:
I asked about the 400 volts. He tried my volt ohm meter. He tossed it into the can. I asked, "So I can finally buy the digital model my wife told me I could not have?". Redeeming himself for not catching the unusual wiring, he said, "YEP!"
#20
Member
Join Date: Jan 2008
Location: Southeastern Pennsylvania
Posts: 3,313
Received 116 Upvotes
on
107 Posts
Wow! That’s great. There should be some kind of law that says if people do non-standard things they should at least mark it clearly or be whipped in public (lol). My house was built in 1967 and I’m finding some real funny (or maybe not so funny) things also. I guess back then there weren’t any forums like this where people would have found out they were definitely doing something wrong.
But all’s well that ends well. Good!
But all’s well that ends well. Good!