30 AMP air compressor and NEMA 10-30?
Hi Folks,
Lets assume I have a large air compressor that require a 30amp breaker. Is is okay to wire the motor for use with a NEMA 10-30 receptacle (dryer) which I already have one installed? Or do I really need to use a 6-30?
Thanks!
Lets assume I have a large air compressor that require a 30amp breaker. Is is okay to wire the motor for use with a NEMA 10-30 receptacle (dryer) which I already have one installed? Or do I really need to use a 6-30?
Thanks!
#2
You really need two hots and a ground. The receptacle probably has two hots and a neutral. A neutral really shouldn't be used as a ground. How is the receptacle wired. Does it have a green or bare or is it wired with a white neutral? Is it connected to the panel by continuous conduit so it could be swapped out for a 14-30R? Is it from a subpanel or from the main panel (first OCPD).
#4
Member
Thread Starter
Join Date: Jul 2012
Posts: 6
Received 0 Votes
on
0 Posts
Should also mention that I have two slots left in the subpanel, so I can add another 30amp breaker and wire whatever is most appropriate. I'm just not sure what is "most appropriate" for a compressor.
#5
Grounds should be separated from neutral in a modern subpanel. That is four wires supplying the subpanel. The subpanel will have an isolated neutral and bonded ground. If that is the case with your subpanel I would recommend running a new circuit. You can use 10-2 and remark the white red (or black or any color but white, gray, or green).