Adding outlet to a three way switch
I have dedicated circuit to pier lights that operate from a switch at the pier and a switch on the porch. Power comes from the panel to a box in the crawl space with two different lines going to each switch. Set up below. I would like to add an outlet operated by both switches. Can I come of the box in the crawl space to do that? Hoepfully the picture attached.

Last edited by ray2047; 07-30-12 at 12:05 PM. Reason: Correct image orentation.
#2
I have dedicated circuit to pier lights that operate from a switch at the pier and a switch on the porch. Power comes from the panel to a box in the crawl space with two different lines going to each switch. Set up below. I would like to add an outlet operated by both switches. Can I come of the box in the crawl space to do that?
Tech Note: To be code compliant, the ungrounded power from the panel (the black wire) should be spliced to the white wire going to the porch switch. That white wire should be marked with black electrical tape or a permanent black marker at each end to show that it has been re-purposed as a conductor for ungrounded power, and it should be connected to the point, or common, terminal on the porch switch. The black wire at that switch should be attached to one of the traveler terminals and, in the crawl space box, spliced to the black wire going to the pier switch.
Short version is mark the white wire at both ends - porch switch box and crawl space box. Swap the terminations for the white wire and the black wire in both boxes.
#3
Member
Sorry I don't have time to look at this in-depth but check this video to see if his method could work for you.
https://www.youtube.com/watch?v=DgcyYsl11dI
Remember to check local codes as always!
https://www.youtube.com/watch?v=DgcyYsl11dI
Remember to check local codes as always!
#4
Member
Thread Starter
Join Date: Aug 2011
Location: USA
Posts: 13
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks Nash, i will add the black tape to note the hot. No sure why the electrician who did the house did not do that.
Arg, that gives me hope, but I want the outlet to be controled by the two switches as well, not always hot. The plan is to add some low voltage lights that are activated when the pier lights are turne on. i want to put the transformer for the 12v lights uner the deck at the house.
Arg, that gives me hope, but I want the outlet to be controled by the two switches as well, not always hot. The plan is to add some low voltage lights that are activated when the pier lights are turne on. i want to put the transformer for the 12v lights uner the deck at the house.
#5
Member
Sorry I took a look later last night and when I drew it out I saw that your diagram (as I understand it) included ground and neutral which on first glance I thought were ungrounded conductors.
I've attached a diagram showing that you can add a conductor from the existing load side of the pier switch, or you can connect to the travelers in the crawl space box and split a duplex, which would give you power all the time there, but only switched from the porch in a code-compliant but less than helpful fashion for what you are trying to do.
Have you considered putting the landscape lighting on a timer or photocell, or both? I used to have a setup like that, so the photocell turned the lights on at dusk and the timer turned them off at 2 AM or whatever.
I've attached a diagram showing that you can add a conductor from the existing load side of the pier switch, or you can connect to the travelers in the crawl space box and split a duplex, which would give you power all the time there, but only switched from the porch in a code-compliant but less than helpful fashion for what you are trying to do.
Have you considered putting the landscape lighting on a timer or photocell, or both? I used to have a setup like that, so the photocell turned the lights on at dusk and the timer turned them off at 2 AM or whatever.

#6
Thanks Nash, i will add the black tape to note the hot. No sure why the electrician who did the house did not do that.
The plan is to add some low voltage lights that are activated when the pier lights are turne on. i want to put the transformer for the 12v lights uner the deck at the house.
#7
Member
Thread Starter
Join Date: Aug 2011
Location: USA
Posts: 13
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Direct burial to a box right before the pier where a shut off for the water is located. from there it runs in conduit along with two other circuit runs (boat lift and shore power) to a box on the pier with the light switch and lift controls.
I guess the photo cell to control the low voltage is an idea. I have a transformer down at the end of the pier that is on the switch for low voltage lights around the pier head and along the pier to shore. (125') I wanted to put another transformer up by the house that would work off the same switch to have low voltage lighting on the path to the house and up the steps.
It would be nice coming back off the water when it is dark, hitting the switch and having the lights come on along the pier and all the way to the house.
I currently have a 300W transformer on the pier that handles two runs, one aournd the lift and one down the pier. 100' run down the pier and another 100' to the house. I wonder, could I do a 200' run and just up the transformer? Only 5 lights (I think they are only about 3W each) up to the house. Think I have 10g coming down the pier.
I guess the photo cell to control the low voltage is an idea. I have a transformer down at the end of the pier that is on the switch for low voltage lights around the pier head and along the pier to shore. (125') I wanted to put another transformer up by the house that would work off the same switch to have low voltage lighting on the path to the house and up the steps.
It would be nice coming back off the water when it is dark, hitting the switch and having the lights come on along the pier and all the way to the house.
I currently have a 300W transformer on the pier that handles two runs, one aournd the lift and one down the pier. 100' run down the pier and another 100' to the house. I wonder, could I do a 200' run and just up the transformer? Only 5 lights (I think they are only about 3W each) up to the house. Think I have 10g coming down the pier.
#8
How close is the 3-way switch at the pier to any point in the run of lights you want to add? You can T-tap off a transformer to go two ways, so just getting the switched power to a good place to set the xfmr will get the job done.
With the information we have now, it is difficult - for me at least - to visualize your setup.
I currently have a 300W transformer on the pier that handles two runs, one aournd the lift and one down the pier. 100' run down the pier and another 100' to the house. I wonder, could I do a 200' run and just up the transformer?

#9
Member
Thread Starter
Join Date: Aug 2011
Location: USA
Posts: 13
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Sorry I confused you. I tapped in the transformer for the low voltage into the power for the light at the pier. The switch and transformer are right next to each other. When I turn on the pier light the transformer comes on and lights up the low voltage on the pier at the same time.
My misson is to continue the low voltage (5 additonal lights) from the end of the pier up to the house. I originally thought I would need a transformer by the house due the the length of the run from the pier to the house. (200') But, if I just increase the transformer size can I continue the run down the pier up to the house with the additional 5 lights? 5 lights on that run now which is 100'. Another 100' to the house. That would be so easy to do and no other outlet is needed.
My misson is to continue the low voltage (5 additonal lights) from the end of the pier up to the house. I originally thought I would need a transformer by the house due the the length of the run from the pier to the house. (200') But, if I just increase the transformer size can I continue the run down the pier up to the house with the additional 5 lights? 5 lights on that run now which is 100'. Another 100' to the house. That would be so easy to do and no other outlet is needed.
#10
I'm not sure why you would need to change the transformer. What is its rating (nameplate information) and what is the rating of each bulb?
Right now what I think we're seeing is 10 lamps at 3W each = 30W on a transformer capable of supplying up to 300W.
Right now what I think we're seeing is 10 lamps at 3W each = 30W on a transformer capable of supplying up to 300W.
#11
Member
But, if I just increase the transformer size can I continue the run down the pier up to the house with the additional 5 lights? 5 lights on that run now which is 100'. Another 100' to the house. That would be so easy to do and no other outlet is needed.
If you find that the voltage is running well under 12VAC, you may be able to compensate with a "good" transformer. For example I have a Sea Gull 600W that has primaries for both 105-115 VAC and 115-125 VAC. My line voltage is 125 VAC, so by switching to the lower-voltage primary, I can boost my secondary voltage to something around 18 VAC. This can prematurely burn out bulbs, especially incandescent bulbs, close to the transformer, so be aware of that.
#12
Member
Thread Starter
Join Date: Aug 2011
Location: USA
Posts: 13
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks guys! Yea, the length of the run is what worried me. I currently have three legs coming off the transformer. Leg 1 had 4 lights an is about 50', leg 2 has 4 lights and is 50' long, leg 3 has 5 lights and is 100' long. Leg 3 is the one I would continue up to the house and add 5 more lights.
LED lights. Emailed the supplier Overtons to get the specs. Here is a link to the light on their site: Overton's : Horizontal Mini LED Light white beam - Boating & Marine > Electrical > Lighting > Courtesy Lights :
I will double check the AWG on the long leg. I can change it if needed. I also have a meter and can check the end of the current line. You have given me the information to figure this thing out. Thanks! Weekend place and I will be up there this weekend and report back.
LED lights. Emailed the supplier Overtons to get the specs. Here is a link to the light on their site: Overton's : Horizontal Mini LED Light white beam - Boating & Marine > Electrical > Lighting > Courtesy Lights :
I will double check the AWG on the long leg. I can change it if needed. I also have a meter and can check the end of the current line. You have given me the information to figure this thing out. Thanks! Weekend place and I will be up there this weekend and report back.
#13
Emailed the supplier Overtons to get the specs. Here is a link to the light on their site: Overton's : Horizontal Mini LED Light white beam - Boating & Marine > Electrical > Lighting > Courtesy Lights :
You did ask Overton's if they still had some, I hope.

#14
Member
Thread Starter
Join Date: Aug 2011
Location: USA
Posts: 13
Upvotes: 0
Received 0 Upvotes
on
0 Posts
You got me looking again. They are actually Atwood lights. Here is a link to the specs: LED Micro Lights
Draw only.75W. i should be OK with the exisiting transformer. I will see what voltage I have at the end of the long run and go from there. I also did find that Seagull transformer. Nice unit.
Draw only.75W. i should be OK with the exisiting transformer. I will see what voltage I have at the end of the long run and go from there. I also did find that Seagull transformer. Nice unit.
#16
Member
They are actually Atwood lights. Here is a link to the specs: LED Micro Lights
Draw only.75W. i should be OK with the exisiting transformer. I will see what voltage I have at the end of the long run and go from there. I also did find that Seagull transformer. Nice unit.
Draw only.75W. i should be OK with the exisiting transformer. I will see what voltage I have at the end of the long run and go from there. I also did find that Seagull transformer. Nice unit.
#18
Member
Thread Starter
Join Date: Aug 2011
Location: USA
Posts: 13
Upvotes: 0
Received 0 Upvotes
on
0 Posts
OK, got up to the house and discovered I only had a 120W transformer in place. I ordered and got a Seagull 300W with the power boost. That should take care of the long run up to the house. The other two short runs should be fine. Thanks for all your advice guys. Went from thinking I needed a second transformer to a much easier solution.