wiring breaker box

i am installinga new dish washer and microwave with an exhoust hgood, what i need to know is what size wire should i use for the dish washer and the microwave, and also a 20 amp 0r 15 amp for the breaker box i have plenty of room to install seperat circuts
 
Sponsored Links
  #2  
Old 08-10-12, 09:45 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Each needs it's own 20 amp circuit. The dishwasher could share with a garbage disposal but probably not the microwave hood because of the NEC percentage rule for built in appliances. You would use #12 two conductor cable (or conduit with THHN) for each.
 
  #3  
Old 08-10-12, 11:25 AM
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 4,719
Received 29 Votes on 28 Posts
I agree, the over-range microwave definitely needs its own dedicated 20A circuit with 12ga wire. (Some smaller ones may only require a 15A, but if it's ever replaced in the future, you might as well run a 20A circuit not).

I would personally run a 14ga / 15A circuit for the dishwasher. Save a few bucks on wire unless it's cheaper/easier to use leftover 12ga. (Ray, let me know if I'm missing something important).
 
  #4  
Old 08-10-12, 12:13 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
I was thinking 20a for the dishwasher if you don't have a garbage disposer now as future proofing if you ever want one. Of course if you already have a dedicated GD feed then you may be able to use that for the dishwasher also.
 
  #5  
Old 08-10-12, 02:25 PM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,493
Received 33 Votes on 25 Posts
The cost difference between #14 and #12 wiring is not enough to justify NOT putting in a 20 ampere circuit for the dishwasher. The microwave oven requires a 20 ampere circuit.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: