Neutral and ground wire size from generator
I'm installing a 7 Kw pad generator and the recomended minimum wire size is 10 AWG. I think I want to use 8 AWG for the 50 foot lengh to reduce voltage loss.
The generator has a two pole 30 amp breaker to feed to my transferr switch. Most of my loads will be 110 volt so will the neutral wire carry 60 amps if I'm at maximum load? There is a ground (green) wire also in the feed. Does that ground wire carry any of the load from the neutral wire?
The generator has a two pole 30 amp breaker to feed to my transferr switch. Most of my loads will be 110 volt so will the neutral wire carry 60 amps if I'm at maximum load? There is a ground (green) wire also in the feed. Does that ground wire carry any of the load from the neutral wire?
#2
The green grounding conductor should only carry current in the event of a fault.
The neutral will carry the difference in current between the two hots. For example, one leg carries 15 amps and the other hot carries 25. The neutral will only see ten amps.
The neutral will carry the difference in current between the two hots. For example, one leg carries 15 amps and the other hot carries 25. The neutral will only see ten amps.
#3
Welcome to the forums!
There should be almost no voltage drop (voltage is never really lost) in a 50' run. Not only is 10AWG rated for 30A, and less expensive, it also offers less resistance than 8AWG.
Your power supply is single-phase 240V. It is carried on two split-phase legs. Connecting either of those legs through a device to a grounded conductor (a neutral) gives a potential of 120V. There is no "110V" in the US. Re 60A on the neutral wire - No.
Not unless there's a wiring fault somewhere.
Wiring Simplified is a valuable resource for learning more about residential electrical systems. It's also inexpensive and available in the electrical aisle at many home improvement centers.
I'm installing a 7 Kw pad generator and the recomended minimum wire size is 10 AWG. I think I want to use 8 AWG for the 50 foot lengh to reduce voltage loss.
The generator has a two pole 30 amp breaker to feed to my transferr switch. Most of my loads will be 110 volt so will the neutral wire carry 60 amps if I'm at maximum load?
There is a ground (green) wire also in the feed. Does that ground wire carry any of the load from the neutral wire?
Wiring Simplified is a valuable resource for learning more about residential electrical systems. It's also inexpensive and available in the electrical aisle at many home improvement centers.
#4
Member
Join Date: Jul 2012
Location: USA
Posts: 46
Upvotes: 0
Received 0 Upvotes
on
0 Posts
my generator back feed has 120 feet of 10/3g, and ran the house fine. I have a you-tube video of it running the house for 7 days when we had the power outage on halloween in 2011. You would think you would get 60 amps , but i guess when one phase is up, the other is down, so you get only 30 amps i think total from each leg, etc. So, if any one of the legs are over 30A, it will trip both i think.
#5
Member
Thread Starter
Join Date: Aug 2012
Posts: 189
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks. I was guessing it could not be 60 amps. So since the currents are out of phase it cancels.
Yes, I meant to say 120 volts. I'm old school and 240,220, 120, 115 and 110 volt were pretty common terms.
Computing voltage drop. Would it be 100 foot of #10 wire since the circuit has to complet both legs?
Yes, I meant to say 120 volts. I'm old school and 240,220, 120, 115 and 110 volt were pretty common terms.
Computing voltage drop. Would it be 100 foot of #10 wire since the circuit has to complet both legs?
#6
Would it be 100 foot of #10 wire since the circuit has to complet both legs?
So since the currents are out of phase it cancels.

#7
Voltage drop is figured on the out and back distance. If you had a receptacle 50' from a panel you would use 100' in the VD calculation.
#8
Member
Thread Starter
Join Date: Aug 2012
Posts: 189
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I ran the numbers at 30 amps. 100 foot of 10 AWG would be 3 volt drop. 100 foot of 8 AWG would be 1.89 volt drop. Looks like 10 AWG will work fine
10 AWG will loose 90 watts and 8 AWG will loose 57 watts at 30 amps.
10 AWG will loose 90 watts and 8 AWG will loose 57 watts at 30 amps.