New Switch Ground
Hello again everyone. I'm in the process of replacing some flakey old 10Amp switches with new 15 amp ones. I'm into a double gang box that is housing two switches. There is one #16 grounding wire entering the box wrapped around a cable clamp screw with another few inches hanging loose. The previous switches were not grounded.

Both of my new switches have grounding terminals - should I ground these switches to the existing grounding wire? Or should I secure the grounding wire to the metal box and run grounding pigtails to the box from each switch? Or do I leave the switches ungrounded?
If it's anything like that #16 wire I found in my receptacle box, it's not really doing anything... (See previous thread on ungrounded receptacles)
Thanks!

Both of my new switches have grounding terminals - should I ground these switches to the existing grounding wire? Or should I secure the grounding wire to the metal box and run grounding pigtails to the box from each switch? Or do I leave the switches ungrounded?
If it's anything like that #16 wire I found in my receptacle box, it's not really doing anything... (See previous thread on ungrounded receptacles)
Thanks!
#2
Have you tested for voltage from hot to neutral, to the ground wire and to the box in this location?
I would bond the ground wire to the box with an approved ground screw, add two pigtails to the end of it, and bond each switch.
I would bond the ground wire to the box with an approved ground screw, add two pigtails to the end of it, and bond each switch.
#3
Member
Thread Starter
Join Date: Jun 2012
Location: USA
Posts: 71
Received 0 Votes
on
0 Posts
Most of the switches in the home are of a similar setup. When I test hot to the ground wire I get about 12-14 volts. Doesn't seem to matter which switch I test, they're all testing the same.
Why would I only be getting 12-14 volts to ground?
Why would I only be getting 12-14 volts to ground?
#4
Switches connected to a grounded metal box are not required to have a separate ground attached to them. You still may do it if you want. Follow Nashkat's post.
Likely the ground wire is not grounded. If this is the case, you will need to address this.
Why would I only be getting 12-14 volts to ground?
#5
Why would I only be getting 12-14 volts to ground?
Do you feel secure in doing some tests inside your panel?
#6
Member
Thread Starter
Join Date: Jun 2012
Location: USA
Posts: 71
Received 0 Votes
on
0 Posts
I don't have any issues with running test in the panel. It's odd though, as there are many receptacles and other items in the home that are properly grounded.
What should I be checking?
What should I be checking?
#7
I was going to suggest tests that would help you determine whether you had an adequate grounding electrode. But given that you say that
here's what I'd look for now:
there are many receptacles and other items in the home that are properly grounded.
- Does your main distribution panel have a main breaker in it, or is that between the meter and the panel?
- Are there separate ground and neutral bars, or are the grounds and neutrals all landed on the same bar(s)?
- Are the neutrals each terminated under a separate screw?
- Are there no more than two grounds under any screw?
- Are all of the ground and neutral screws properly torqued (there should be terminal torgue values listed on the label inside the panel door)?
#8
Member
Thread Starter
Join Date: Jun 2012
Location: USA
Posts: 71
Received 0 Votes
on
0 Posts
The main panel does have a main breaker - 100 amp.
There are not separate neutral/ground bars. Many are combined. I will include a picture below.
Most of the neutrals are under a separate screw, however I believe there are a couple that are combined.
There are a few screws that have numerous grounds.
Not sure on the torque - I would have to check that.
Somewhat random - I did find one ground the was led close to the bar, but not actually attached. This is not on any of the circuits we've been discussing but certainly is a show of the quality of the previous owner when he ran a new circuit. That particular circuit is modern yellow 12/2 NM.

There are not separate neutral/ground bars. Many are combined. I will include a picture below.
Most of the neutrals are under a separate screw, however I believe there are a couple that are combined.
There are a few screws that have numerous grounds.
Not sure on the torque - I would have to check that.
Somewhat random - I did find one ground the was led close to the bar, but not actually attached. This is not on any of the circuits we've been discussing but certainly is a show of the quality of the previous owner when he ran a new circuit. That particular circuit is modern yellow 12/2 NM.


#9
Many errors in the panel. You have many places where you have both ground and neutral in the same hole. You can not have a ground and neutral in the same hole and only one neutral per hole with no more then two grounds per hole. I was trying to find the number of correct connections on the ground and neutral bars but only saw two and those may just look right because of the angle of the camera shot.
#12
What is the make and model of your panel? Is it a Square D QO Loadcenter? If so, finding an add-in ground bar and a replacement for the missing neutral bar section which pcboss pointed out may be fairly easy. I would check with the local supply house that distributes Square D products.
#13
Member
Thread Starter
Join Date: Jun 2012
Location: USA
Posts: 71
Received 0 Votes
on
0 Posts
Thanks everyone. From the research I did, the panel did not come with that segment from the factory. Below is a link to my recent post to discuss that issue.
http://www.doityourself.com/forum/el...utral-bar.html
http://www.doityourself.com/forum/el...utral-bar.html
#14
I thought this panel looked familiar!
Doesn't matter - there's clearly a place already made there to add one if you need it. You may not need it after you get all the grounds moved to a separate bar.
Or you could just install the add-on bar and sort everything out there. But that's only going to give you 36 terminal locations at the most, if I'm reading the panel correctly. While there's no need to separate the grounds and neutrals in this panel, 36 positions is only enough for 24 120V branch circuits. Dropping below 24 will free up a terminal for a pair of grounds. Is that going to be enough for you?
From the research I did, the panel did not come with that segment from the factory.
Or you could just install the add-on bar and sort everything out there. But that's only going to give you 36 terminal locations at the most, if I'm reading the panel correctly. While there's no need to separate the grounds and neutrals in this panel, 36 positions is only enough for 24 120V branch circuits. Dropping below 24 will free up a terminal for a pair of grounds. Is that going to be enough for you?