Lighted Switch Problem

The lighting circuit in my garage has a switch loop, to shut the lights off. The lights are pull-chain florescent lights. The switch is off; the light in the switch is bright. When the switch is still off, and I pull the pull chains on both the lights, (shut them off) the light goes dim, but power is not to them. Seems the switch might be bad, because there is a slight voltage on the top screw. Weird...Is this normal? The outlets test ok ....

First pic - Lights off, pullchains switched on.
Second Pic - Lights off, pullchains switched off.
Third Pic - Lights on, pullchains on.
---------------------------


Name:  switchloop3.jpg
Views: 2082
Size:  34.9 KBName:  switchloop5.jpg
Views: 807
Size:  32.2 KB
[/SIZE]
 
Attached Images  

Last edited by rodog; 08-27-12 at 01:20 PM. Reason: word format
Sponsored Links
  #2  
Old 08-27-12, 01:21 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,594
Your switch may need a neutral for proper operation. An older switch loop does not have a neutral.

With the pull chain off no voltage can trickle through the ballast.

You box should be grounded. How are you measuring voltage? Between what two points?
 
  #3  
Old 08-27-12, 01:36 PM
Banned. Rule And/Or Policy Violation
Join Date: Jan 2010
Location: KS
Posts: 1,896
Nah, the neon style basically just connect the bulb in parallel with the switch contacts. When the switch is off, a small amount of power 'leaks' through the fixture to create a complete circuit, and when the switch is on, the bulb contacts are shorted, which makes the bulb go out. I've never seen one of that style that requires a neutral.

It's actually similar in function to the automotive fuses that light up when they blow. When the fuse is intact, the bulb is shorted, but if the fuse blows, a limited amount of power backfeeds though the load and lights the bulb.
 
  #4  
Old 08-27-12, 11:14 PM
Member
Thread Starter
Join Date: Jul 2012
Location: USA
Posts: 54
cool, i guess ok then..............
 
  #5  
Old 08-28-12, 12:30 PM
Member
Thread Starter
Join Date: Jul 2012
Location: USA
Posts: 54
my friend is the one who checked it, and i think he said something like 40v was coming through. Top post on switch i think.
 
  #6  
Old 08-28-12, 01:30 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
my friend is the one who checked it, and i think he said something like 40v was coming through. Top post on switch i think.
There should be no actual potential on the switch yoke. 40V might be an induced reading.

Did your friend use a digital meter or an analog meter? What was the other probe touching?
 
  #7  
Old 08-28-12, 03:51 PM
Banned. Rule And/Or Policy Violation
Join Date: Jan 2010
Location: KS
Posts: 1,896
With the neon bulb in there you will have current flow with the swtich off because the bulb is in parallel with the switch.
 