I have a 200amp meter/disconnect combination panel on the outside of the house. I need to know where to attache the ground in the box that will run to the UFER. See pics
I'm thinking it will be from the small acorn on the bar on the right side below the disconnect.


Can I use #6 solid copper or do I need #4. Also can the solid copper go thru the same hole (at the bottom of the panel to the basement) that the supply wire will go thru. I'll be placing a 2in metal nipple in that hole to run the wires to the main breaker in the basement.
Thanks for your help
Dano
I'm thinking it will be from the small acorn on the bar on the right side below the disconnect.


Can I use #6 solid copper or do I need #4. Also can the solid copper go thru the same hole (at the bottom of the panel to the basement) that the supply wire will go thru. I'll be placing a 2in metal nipple in that hole to run the wires to the main breaker in the basement.
Thanks for your help
Dano
#2
Ufer grounds are installed in the footings before the house is constructed. It should have been a #4.
A #4 should fit in any hole on the ground/neutral bus.
A #4 should fit in any hole on the ground/neutral bus.
#4
An unspliced #4 is required to an approved clamp on the rebar. If there is a copper already sticking out of the CEE it is going to need an irreversible splice.
#5
Also can the solid copper go thru the same hole (at the bottom of the panel to the basement) that the supply wire will go thru.
I need to know where to attache the ground in the box that will run to the UFER... I'm thinking it will be from the small acorn on the bar on the right side below the disconnect.
Last edited by Nashkat1; 08-29-12 at 11:48 AM. Reason: to correct an inaccuracy
#6
I'll be placing a 2in metal nipple in that hole to run the wires to the main breaker in the basement.