Mixed wiring sizes

I was checking the wiring in my house to add more receptacles and I noticed a couple of the circuits installed by previous homeowners in my house started off with 12-2 romex and from the first receptacle the 12-2 goes to,it steps down to 14-2 romex,however the cable from the panel to the receptacles are on a 15 amp breaker.Is this code? I heard it was and it wasn't from different google results and people I asked.
 
Sponsored Links
  #2  
Old 09-22-12, 08:20 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,644
So long as the breaker is small enough to protect the smallest wire it is code bu not recommended because it can cause confusion about the size breaker to use. Someone seeing just the #12 portion might mistakenly think they can use a 20 amp breaker.
 
  #3  
Old 09-22-12, 05:26 PM
Member
Thread Starter
Join Date: Feb 2012
Location: United States
Posts: 68
Someone seeing just the #12 portion might mistakenly think they can use a 20 amp breaker.
That's what I thought,I'm going to change it all to 12-2 since I have a box of cable,thank you.
 