Neutral ground bar in main panel
I've installed a 100amp subpanel in my workshop. I'm using 2-2-2-4 trailer feed cable for my conductors. The Subpanel is being fed from a 60amp breaker in my main panel. It's an Eaton Cutler Hammer brand panel and uses 1 neutral ground bar for the neutral and grounds. The problem is that all the spaces on the bar are full. It has tapped mounting holes for an additional bar, so I went that route. I've mounted the bar directly to the can and I've mounted the appropriate sized lugs for the #2 wire. My question is, is it sufficient to have the bar mounted directly to the box, or is it necessary to bond it with a #6 copper wire to the original neutral ground bar.
#2
The additional mounting spots are for ground bars. You can't use an add-on ground bar for neutrals. What you need to do is remove some of the grounds from the neutral bus and move them to the new ground bar. You can extend them if needed.
#5
Member
Thread Starter
Join Date: Sep 2012
Location: United States
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Sorry. I should have been more specific in my original post. The neutrals and grounds are separated and not bonded in the sub. It's the main panel that has no room on the neutral ground bar
#6
It's the main panel that has no room on the neutral ground bar
#9
Should I scuff some of the paint off in the box where the new ground bar makes contact?