Blow dryer killed the outlet? How can I fix it?
Hello,
I'm new here and wanted to say hello - I also need help and hope someone could help. I don't know much about electricity.
Basically, mom was using the blow dryer when the outlet she had the blow dyer plugged in went dead.
The breaker did not trip. We have a light switch that controls the outlet and only this outlet. All other outlets in the room work.
What I have done so far:
1) Tested the outlet with a voltage tester - Power light of the tester does not come on (no power)
2) I've changed the outlet and tested it - Still no power
3) Tested each breaker in the basement - they all seem to work
4) Tested the light switch - no power
5) Replaced the light switch and tested it - no power
6) Removed the outlet and light switch and tested all the wires separately - still no power
There is a black and red wire that go into the outlet. There is no neutral wire going to the green screw. Currently, the black wire is on top right side (bronze) and the red wire is on top left (silver side).
There are 2 black and 2 red wires for the light switch that turns the outlet on or off. I believe it's called single pole? One screw on top and one on bottom. Both screws are on the right side. Currently, one black wire is screwed into the top and one to the bottom. There is no neutral wire going into the green screw. And the 2 red wires are twisted together and capped. I don't see why anything needs to be switched around with the wires, but I was desperate so I even tried screwing both black wires to the bottom of the switch and screwing one of the red ones to the top screw. It didn't work.
Some pictures of the light switch below. I did not take pix of the outlet since it just has one black wire and one red wire.
ImageShack® - Online Photo and Video Hosting
ImageShack® - Online Photo and Video Hosting
Thank you very much
I'm new here and wanted to say hello - I also need help and hope someone could help. I don't know much about electricity.
Basically, mom was using the blow dryer when the outlet she had the blow dyer plugged in went dead.

What I have done so far:
1) Tested the outlet with a voltage tester - Power light of the tester does not come on (no power)
2) I've changed the outlet and tested it - Still no power
3) Tested each breaker in the basement - they all seem to work
4) Tested the light switch - no power
5) Replaced the light switch and tested it - no power
6) Removed the outlet and light switch and tested all the wires separately - still no power
There is a black and red wire that go into the outlet. There is no neutral wire going to the green screw. Currently, the black wire is on top right side (bronze) and the red wire is on top left (silver side).
There are 2 black and 2 red wires for the light switch that turns the outlet on or off. I believe it's called single pole? One screw on top and one on bottom. Both screws are on the right side. Currently, one black wire is screwed into the top and one to the bottom. There is no neutral wire going into the green screw. And the 2 red wires are twisted together and capped. I don't see why anything needs to be switched around with the wires, but I was desperate so I even tried screwing both black wires to the bottom of the switch and screwing one of the red ones to the top screw. It didn't work.
Some pictures of the light switch below. I did not take pix of the outlet since it just has one black wire and one red wire.
ImageShack® - Online Photo and Video Hosting
ImageShack® - Online Photo and Video Hosting
Thank you very much

#2
Welcome to the forums! Neutrals don't go to the grounding screws. The "red" wires you refer to are "white" and are your neutrals. If you note they were twisted together to each other. The blacks have loops in them and were attached to your switch, one on top and one on bottom, and it doesn't matter which way. With the wires pulled out as you have them, can you restore power to the switch via the breaker and determine if you have power there?
Do you have GFCI protection in any other room adjacent to this one, or on the outside of the house close to this location?
Do you have GFCI protection in any other room adjacent to this one, or on the outside of the house close to this location?
#3
Member
Thread Starter
Join Date: Sep 2012
Location: USA
Posts: 10
Received 0 Votes
on
0 Posts
Thanks for responding. I've turned each breaker off and on and tested the two black wires from the switch. There is no power.
I have a GFI outlet in the bathroom adjacent to this bedroom. An electrician installed it last year. I've tested and resetted the GFI. Do I need to do anything else?
I have a GFI outlet in the bathroom adjacent to this bedroom. An electrician installed it last year. I've tested and resetted the GFI. Do I need to do anything else?
#6
Then you may not have found the correct GFCI yet. It could be anywhere inside or outside the house or hidden and forgotten behind something that hasn't been moved in years.
There should not be. That is not how you test for power. Using an analog multimeter or test light test between each black and each neutral (white). Do NOT use a non-contact tester. It is useless for this kind of testing.
tested the two black wires from the switch. There is no power.
#7
Member
Thread Starter
Join Date: Sep 2012
Location: USA
Posts: 10
Received 0 Votes
on
0 Posts
Ok - I just did a walk through of the whole house and did not find any other GFIs; not surprising since the house is from the early 50s.
I am using this - Is this the right tool? By the way, I tested the wires from two other light switches and outlets in the house using this tool and they worked.
110/220 VAC Voltage Tester-MS8900H at The Home Depot
I am using this - Is this the right tool? By the way, I tested the wires from two other light switches and outlets in the house using this tool and they worked.
110/220 VAC Voltage Tester-MS8900H at The Home Depot
#9
Member
Thread Starter
Join Date: Sep 2012
Location: USA
Posts: 10
Received 0 Votes
on
0 Posts
I have turned the breakers on and off many times while I was playing with the wires. I don't even know which is the right breaker for this outlet, so I've shut down the Main too to be safe.
Could the problem be inside the walls or something?
Could the problem be inside the walls or something?
#10
Tester is correct. What were the results of the tests I asked you to make. Do you have a "3-prong" receptacle with a known good ground? If so run an extension cord from there to the switch box and repeat the tests, this time between the extension cord ground and each wire in the switch box.
#11
Member
Thread Starter
Join Date: Sep 2012
Location: USA
Posts: 10
Received 0 Votes
on
0 Posts
I don't have a multimeter, unfortunately. I used the tool I got from HD (link below) to test the wires and it showed no power.
The only 3 prong receptacle with a ground is the new GFI outlet in the bathroom. Do you want me to plug a 3-prong extension cord to the GFI outlet and then you said from there to the switch box? Am I understanding this correctly? How do I do that? The other end of the extension cord has receptacles...
The only 3 prong receptacle with a ground is the new GFI outlet in the bathroom. Do you want me to plug a 3-prong extension cord to the GFI outlet and then you said from there to the switch box? Am I understanding this correctly? How do I do that? The other end of the extension cord has receptacles...
#12
I don't have a multimeter, unfortunately. I used the tool I got from HD (link below) to test the wires and it showed no power.
- First, plug your tester leads into a known good receptacle to make sure the tester is working;
- Turn off the power, remove the switch and separate the wires attached to it. Pull the neutrals splice forward, remove the wire nut, and position the uncovered splice well away from the two black wires;
- At the panel, make sure all the breakers are on. To do that, turn every breaker that you think might be supplying the bathroom all the way OFF and then all the way ON - a tripped breaker is not off. it is tripped, and must be turned off before it can be reset;
- At the switch box, test between each of the black wires and the pair of neutrals; if the box is metal, test between each black wire and the box.
#13
Member
Thread Starter
Join Date: Sep 2012
Location: USA
Posts: 10
Received 0 Votes
on
0 Posts
Nashkat1 -
Thanks, I did everything you said and read the guide you linked to before I posted. Still a no go. What did you mean by "a loose connection at the next device upline"? You mean another outlet in the same room? Other outlets in the room work. How do I check?
I got a quote from an electrician. The estimate says: "Fix (1) existing duplex outlet with missing neutral." Does that mean anything to anyone?
I'm still also interested in Ray's comments but I don't think I understood it correctly.
I'm about to go bonkers.
Thanks, I did everything you said and read the guide you linked to before I posted. Still a no go. What did you mean by "a loose connection at the next device upline"? You mean another outlet in the same room? Other outlets in the room work. How do I check?
I got a quote from an electrician. The estimate says: "Fix (1) existing duplex outlet with missing neutral." Does that mean anything to anyone?
I'm still also interested in Ray's comments but I don't think I understood it correctly.
I'm about to go bonkers.

#15
What did you mean by "a loose connection at the next device upline"? You mean another outlet in the same room? Other outlets in the room work. How do I check?
#16
I got a quote from an electrician. The estimate says: "Fix (1) existing duplex outlet with missing neutral." Does that mean anything to anyone?
#17
Member
Thread Starter
Join Date: Sep 2012
Location: USA
Posts: 10
Received 0 Votes
on
0 Posts
Ray -
You were saying something about running an extension cord but I didn't understand the instructions, so I had responded with: The only 3 prong receptacle with a ground is the new GFI outlet in the bathroom. Do you want me to plug a 3-prong extension cord to the GFI outlet and then you said from there to the switch box? Am I understanding this correctly? How do I do that? The other end of the extension cord has receptacles...
Thanks George - I'm thinking all of this might be beyond me and to just bite the bullet and hire an electrician or just leave the outlet alone. I'm gonna try to get one of those outlet testers over the weekend though.
You were saying something about running an extension cord but I didn't understand the instructions, so I had responded with: The only 3 prong receptacle with a ground is the new GFI outlet in the bathroom. Do you want me to plug a 3-prong extension cord to the GFI outlet and then you said from there to the switch box? Am I understanding this correctly? How do I do that? The other end of the extension cord has receptacles...
Thanks George - I'm thinking all of this might be beyond me and to just bite the bullet and hire an electrician or just leave the outlet alone. I'm gonna try to get one of those outlet testers over the weekend though.
#18
The cord is used as a ground reference to check each of the black and white wires in the switch box. This is done with the wires disconnected. Sometimes this will identify an open (bad) neutral. Given the age of the house though the GFCI may not be grounded so you first need to check for voltage between the narrow slot of the GFCI and the ground of the GFCI to see if it is grounded.
#19
Member
Thread Starter
Join Date: Sep 2012
Location: USA
Posts: 10
Received 0 Votes
on
0 Posts
So what to I have to do exactly with the extension cord? I still don't follow, sorry.
Thanks.
With the GFI, when I put the black probe in the ground hole and the red in the right hole, the tester lights up. It also lights up with I put the black probe in the left hole and the red one in the right hole. Is this a good thing? Thanks.

With the GFI, when I put the black probe in the ground hole and the red in the right hole, the tester lights up. It also lights up with I put the black probe in the left hole and the red one in the right hole. Is this a good thing? Thanks.
#20
There is no left and right hole. A receptacle can be oriented anyway you want, ground on top, ground on bottom, even sideways.There is the wide neutral slot, the narrow ungrounded conductor slot (hot) and (in newer receptacles) the semi-round ground hole. (In your receptacles probably no ground hole.)
In a properly functioning circuit you should have 120 volts between hot and neutral and 120 volts between hot and ground. If you don't get 120 volts between hot and neutral but do get 120 volts between hot and ground that indicates the hot is good but the neutral is bad. Obviously you need a ground to do the test. If no ground at the receptacle you must get a ground from somewhere else. An extension cord in a properly grounded receptacle is one way to do this.
In a properly functioning circuit you should have 120 volts between hot and neutral and 120 volts between hot and ground. If you don't get 120 volts between hot and neutral but do get 120 volts between hot and ground that indicates the hot is good but the neutral is bad. Obviously you need a ground to do the test. If no ground at the receptacle you must get a ground from somewhere else. An extension cord in a properly grounded receptacle is one way to do this.
#21
With the GFI, when I put the black probe in the ground hole and the red in the right hole, the tester lights up. It also lights up with I put the black probe in the left hole and the red one in the right hole. Is this a good thing?