From range to cooktop plus oven

Hey all,
I'm reno'ing my kitchen and as part of the upgrade I'm switching from a standard range to an induction cooktop and convection oven. My question regards the wiring for them. I currently have a 40amp breaker with a #8 wire (8/3 + gnd). Can I branch from the current outlet to supply the new appliances without having to change the wire or breaker? The new appliances are as follows:
Cooktop - 2-3.2kW elements, 1-1.8kW element, 1-1.4kW element (9.6Kw total)
Oven - 5.1kW

If I do need to add a breaker, can I use the 8/3 40amp for the cooktop and add __________ for the oven? Or do I need to use the 8/3 for the oven and add _________ for the cooktop? It's about a 50' (15m) run from the kitchen to the breaker panel.

Thanks,
Rene
 
Sponsored Links
  #2  
Old 10-01-12, 02:45 PM
tldoug's Avatar
Member
Join Date: Jan 2009
Location: USA
Posts: 317
These appliances need to be on separate circuits. The 40 amp breaker should be adequate for the oven. Check the installation manual for the cooktop to see if a 50 amp or 60 amp breaker is recommended.
 