Conduit depth in concrete

Reply

  #1  
Old 10-01-12, 12:11 PM
Member
Thread Starter
Join Date: Sep 2012
Location: USA
Posts: 5
Conduit depth in concrete

Is there anything in the code that gives a depth requirement for putting conduit in concrete?
 

Last edited by Nashkat1; 10-01-12 at 03:12 PM.
Sponsored Links
  #2  
Old 10-01-12, 05:48 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
Is this under a building?
 
  #3  
Old 10-01-12, 07:58 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 11,979
As Justin brought up, if it is under a building it is 0", it can be in the pour. If not, it varies by wiring method. Where are putting the conduit and what is the conduit material?
 
  #4  
Old 10-02-12, 08:41 AM
Glennsparky's Avatar
Member
Join Date: Nov 2011
Location: USA
Posts: 136
Table 300.5, page 70-138 in the 2011 code.
 
  #5  
Old 10-02-12, 10:05 AM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
Table 300.5, page 70-138 in the 2011 code.
I really wish Table 300.5 listed "In an interior slab" or "Encased in a concrete floor not subject to vehicular traffic," or something like that, rather than just "Under a building," for one of the locations.
 