3-conductor 240V outlet on a subpanel


  #1  
Old 12-02-12, 07:13 AM
N
Member
Thread Starter
Join Date: Mar 2002
Location: USA
Posts: 146
Upvotes: 0
Received 0 Upvotes on 0 Posts
3-conductor 240V outlet on a subpanel

I'm wiring a 240V, three-conductor outlet for a welder in the garage. I'll run a dedicated circuit for the outlet. The breaker box is a subpanel.

When I wire the third conductor, do I wire it to neutral, or to ground? This doesn't matter in a main panel since ground and neutral are bonded in the main panel, but this is the first time I've faced this situation on a subpanel.
 

Last edited by pcboss; 12-02-12 at 07:29 AM.
  #2  
Old 12-02-12, 07:19 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,332
Received 877 Upvotes on 740 Posts
The third wire is a ground and therefore should be connected to the ground buss.
 
 