[Ground Rod] location

When running service to a detached building, does it matter if the grounding rod is inside the building or outside? The floor of the buildings field stone laid in a thin concreate bed that is failing in spots so it may be possible to sink the rod inside the building.

Thanks

pagebu
 

Last edited by ray2047; 10-10-12 at 07:55 PM. Reason: Correct title.
Sponsored Links
  #2  
Old 10-10-12, 07:50 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
It needs to be where it'll be permanently moist.
 
  #3  
Old 10-11-12, 05:24 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,354
I don't think the NEC prohibits installing the ground rod inside through the floor, but I would rather have it outside.
 
  #4  
Old 10-11-12, 05:28 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: USA
Posts: 17,607
Are you supposed to have a ground rod? I thought that may take away from the main homes ground rod, or something like that?

Just asking.....
 
  #5  
Old 10-11-12, 05:40 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,987
Any detached building served by a feeder must have at least one grounding electrode, usually a ground rod or ufer. Often two ground rods are used to avoid having to prove one is enough. (Article 250 NEC).

A multiwire branch circuit to an outbuilding is considered a single circuit and no electrode is needed.

Also a means of disconnect is required.
 

Last edited by pcboss; 10-11-12 at 05:52 PM. Reason: expanded on original post
  #6  
Old 10-12-12, 09:31 AM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
Are you supposed to have a ground rod? I thought that may take away from the main homes ground rod, or something like that?
If you're creating a subpanel in the detached structure, then yes. It will add to, or supplement, the service entrance grounding.
 