Welder not working. no ground? quickwire setup?
#1
Member
Thread Starter
Join Date: Sep 2012
Location: The States
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Welder not working. no ground? quickwire setup?
for xmass one year i got a Chicago 220v 90amp mig welder.
220v 25amp breaker minimum.
wires: black, red, green.
I plugged it in to my 220v 30 amp dry recepticle and the light came on but nothing else happened. I think because the wiring for the dryer is red black white and there is no ground bar in the Breaker box.
is that the issue and can a ground bar be added?
220v 25amp breaker minimum.
wires: black, red, green.
I plugged it in to my 220v 30 amp dry recepticle and the light came on but nothing else happened. I think because the wiring for the dryer is red black white and there is no ground bar in the Breaker box.
is that the issue and can a ground bar be added?
#3
Member
Join Date: Oct 2012
Location: USA
Posts: 550
Upvotes: 0
Received 0 Upvotes
on
0 Posts
can I hook up the 2 hotwires to the recepticle and push the ground wire on the welder in to the ground?
Do you mean push it into the ground as in 'the dirt'? No, don't do that.
#4
No ground or neutral are needed for a 240 volt device to function*. You only need two 240 volt hots.
The red and black are the two wires you need to run the welder. The white** is not used.
If it is the main panel (first OCPD) it usually won't.
Your problem is definitely not a ground problem. It is probably how you wired the plug. The welder should be connected only to the brass screws of the plug. I would not use the dryer receptacle because there is no safe way to connect the ground.
*Ground is only for safety and only carries current in case of fault.
** White is a combined neutral ground on a 3-wire dryer circuit.
dryer is red black white
there is no ground bar in the breaker box.
Your problem is definitely not a ground problem. It is probably how you wired the plug. The welder should be connected only to the brass screws of the plug. I would not use the dryer receptacle because there is no safe way to connect the ground.
*Ground is only for safety and only carries current in case of fault.
** White is a combined neutral ground on a 3-wire dryer circuit.
#7
Group Moderator
Are you certain your welder is a 240 volt model? The only Chicago Electric 90 amp mig welder I see on the Harbor Freight website is 120 volts.
#9
Yeah, Pilot Dane is right, I have one of those. Model #68887 is a 120V flux wire welder. Should be plugged directly into a dedicated 20 Amp 120V circuit for best results.
wires: black, red, green.
#10
Member
Thread Starter
Join Date: Sep 2012
Location: The States
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I copied this from the owners manual so yes its 220v (240)
PRODUCTSPECIFICATIONS
Welding Current 30 ~ 110 Amps
Duty Cycle 15% @ 110 Amps / 100% @ 30 Amps
(Refer to chart and explanation on page 18)
Power Consumption 220 Volt / 60 Hz / Single Phase / 24.5 Amps
(Should be connected to a 25 Amp minimum dedicated circuit)
Open Circuit Voltage 40 Volts Maximum
Required Power Plug Type 3-Prong, 220 VAC, polarized, twist lock (not included)
NEMA#L6-30 or equivalent
Power Cord Rating 14 AWG x 3C x 6’Long
Gas Inlet Size 1
/
4
”
Cables Ground: 6 Gauge, 6’.................Torch: 8 Gauge, 6’
Welding Wire Size 0.23” to 0.035”
Wire Spool Size 4” Diameter
Included Torch Tip Size 0.030”
Accessories Wire Spool / Cylinder Strap / Wire Brush & Hammer /
Spare .8mm & 1.0mm Welding Tips / Hand-Held Face Shield
Net Weight 53.5 Pounds
Revise to: “ .6mm & .9mm”
PRODUCTSPECIFICATIONS
Welding Current 30 ~ 110 Amps
Duty Cycle 15% @ 110 Amps / 100% @ 30 Amps
(Refer to chart and explanation on page 18)
Power Consumption 220 Volt / 60 Hz / Single Phase / 24.5 Amps
(Should be connected to a 25 Amp minimum dedicated circuit)
Open Circuit Voltage 40 Volts Maximum
Required Power Plug Type 3-Prong, 220 VAC, polarized, twist lock (not included)
NEMA#L6-30 or equivalent
Power Cord Rating 14 AWG x 3C x 6’Long
Gas Inlet Size 1
/
4
”
Cables Ground: 6 Gauge, 6’.................Torch: 8 Gauge, 6’
Welding Wire Size 0.23” to 0.035”
Wire Spool Size 4” Diameter
Included Torch Tip Size 0.030”
Accessories Wire Spool / Cylinder Strap / Wire Brush & Hammer /
Spare .8mm & 1.0mm Welding Tips / Hand-Held Face Shield
Net Weight 53.5 Pounds
Revise to: “ .6mm & .9mm”
#12
Group Moderator
Time to get out your volt meter, open it up and start testing for what's wrong. I'd start at the power cord coming in and check for continuity and follow the power through the unit looking for anything blown.
#13
I was looking this over and I'm not sure where we left off.
You plugged the unit in and a light on it turned on......correct ?
Which means you've installed a plug on the cord with a matching receptacle ?
Do you have a volt/ohmmeter ?
You plugged the unit in and a light on it turned on......correct ?
Which means you've installed a plug on the cord with a matching receptacle ?
Do you have a volt/ohmmeter ?
#14
the light came on
Is the drier receptacle 3 slot or 4 slot?
#17
You will need to connect the welder to the house with three wires. Two hot wires like red and black. Then you'll need to connect the green ground wire. The welder will run with or without the ground wire. It does not need the ground to operate. The ground wire is used in case something shorts inside the welder and touches the case.
Actually.....on edit. I'll correct myself. That welder may require the green wire to be connected as it may have 110v control circuits in it.
Actually.....on edit. I'll correct myself. That welder may require the green wire to be connected as it may have 110v control circuits in it.
Last edited by PJmax; 10-28-12 at 01:26 PM. Reason: further info
#18
Group Moderator
#19
So I dont use ground or what?
there is no ground bar in the Breaker box.
Are you talking about your main panel?
#20
Actually.....on edit. I'll correct myself. That welder may require the ground to be connected. It may have 110v control circuits in it.
Can you give us a model number or better yet link to an on line manual for it?
Last edited by ray2047; 10-28-12 at 02:03 PM.
#21
I updated my previous post but this is a mig welder I believe so it has a variable speed control board for wire feed and possible shielding gas valve control functions. Those devices may run on 120v. not 240v. Just a guess as I haven't seen nor can I find any wiring info on it.
#22
I updated my previous post but this is a mig welder I believe so it has a variable speed control board for wire feed and possible shielding gas valve control functions. Those devices may run on 120v. not 240v. Just a guess as I haven't seen nor can I find any wiring info on it.
Power Consumption 220 Volt / 60 Hz / Single Phase / 24.5 Amps
Has this welder ever worked before?
#23
Good point Joe but when you buy an electric dryer it says it requires 240volt, nothing about 120/240 but we know that it actually requires 120/240. Heating element is 240v and the rest including the controls are 120v. See my point ?
#24
Good point Joe but when you buy an electric dryer it says it requires 240volt, nothing about 120/240 but we know that it actually requires 120/240. Heating element is 240v and the rest including the controls are 120v. See my point ?
#25
Forum Topic Moderator
I have never seen a welder that needed a 4 wire connection

#26
About 10-12 yrs ago a friend of mine bought a 220 volt arc welder that had a 4 prong plug.
#27
Group Moderator
I'm still curious if the welder has ever worked or if this is the first time it has been powered up? I'm trying to figure out if it's a "how to wire it up" issue or a bad welder that needs debugging.
#28
As Dane pointed out the O/P hasn't answered the main questions:
Has it ever worked?
How did you wire the plug? Was it the black and red on brass?
How is the dryer receptacle wired?
Has it ever worked?
How did you wire the plug? Was it the black and red on brass?
How is the dryer receptacle wired?