Using existing cable for ceiling fan


  #1  
Old 10-24-12, 05:12 AM
B
Member
Thread Starter
Join Date: Oct 2012
Location: USA
Posts: 10
Upvotes: 0
Received 0 Upvotes on 0 Posts
Using existing cable for ceiling fan

I have a light fixture that currently has one 12-2 cable from the switch to the fixture. I would like to put in a ceiling fan.

Can two 12-2 cables be used instead of one 12-3 cable for controlling a ceiling fan and light separately(one switch for the light, one for the fan)? Can I just tie the neutrals and grounds together on each end? Thanks.
 
  #2  
Old 10-24-12, 06:27 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Just as easy to run a new three conductor cable as a new two conductor cable but either way would be code compliant. The existing cable can be abandoned by cutting it as short as possible on both ends and shoving it out of bot the ceiling box and switch box. No need to remove the cable other then that.

The ceiling box you have is probably not fan rated so it will probably need to be changes out also. If your not sure post a picture but if it use 8-32 screws to mount fixtures it is almost certainly not fan rated.
 

Last edited by ray2047; 10-24-12 at 09:49 AM. Reason: Add omitted word.
  #3  
Old 10-24-12, 06:29 AM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,874
Received 372 Upvotes on 332 Posts
Yes, you can use two 12/2 cables. Tie the grounds and neutrals together at the switch, but you must keep the neutrals separate at the fan/light. So the fan hot/neutral would be connected to one cable while the light hot/neutral is connected to the other wire. All grounds are tied together at the switch and fan.

You likely will have to replace the box too. You need to use a fan-rated box that's securely attached to the joists. Most fan boxes can be installed without removing any drywall though.

They also have remote controlled fans these days, you just provide power to the fan and the remote control handles the fan, light, speed, etc. Just as another option.
 
  #4  
Old 10-24-12, 07:40 AM
B
Member
Thread Starter
Join Date: Oct 2012
Location: USA
Posts: 10
Upvotes: 0
Received 0 Upvotes on 0 Posts
Just as easy to run a new three conductor cable as a new two conductor cable but either way would be code compliant.
I already have the 12/2 but I would have to purchase the 12/3.

The ceiling box you have is probably not fan rated so it will probably need to be changes out also.
The ceiling box is definitely not fan rated. Fortunately, installing a ceiling fan rated box should be fairly easy, as the attic is not insulated yet over the room(used to be a garage.) Can I purchase any octagonal metal electrical box that attaches to the joist, or MUST it say "ceiling fan rated."
 

Last edited by ray2047; 10-24-12 at 09:48 AM. Reason: Fix quote for clarity.
  #5  
Old 10-24-12, 07:45 AM
S
Group Moderator
Join Date: Oct 2004
Location: WI/MN
Posts: 18,893
Received 1,197 Upvotes on 1,152 Posts
You want one that says ceiling fan rated.
 
 