I am looking at having a whole house surge protector added to our home.
Looking at the manual, is says put it on it's own breaker near the top/power feed.
I am not able to put the breaker near the top.. Only spot I got is mid way.... Am I going to take risk of breakers that are above it, and items below it will be protected?
Looking at the manual, is says put it on it's own breaker near the top/power feed.
I am not able to put the breaker near the top.. Only spot I got is mid way.... Am I going to take risk of breakers that are above it, and items below it will be protected?
#2
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Having the surge arrestor as close as possible to the incoming feed is ideal but you should be fine with it connected to circuit breakers in the middle of the bus.
What brand/model are you installing?
What brand/model are you installing?
#4
Jay, if you're worried about warranty stuff, you could always pigtail the top breaker(s) down to the mid point and install the breaker for the surge protector at the top. What breakers do you have at the top and what are their amperage?
#5
On top, I have the 30 amp A/C breaker on the left, and on right I have the 15 amp kitchen outlets.
I have thought of dropping everything on the left down. So Surge on top, A/C next down..
I have thought of dropping everything on the left down. So Surge on top, A/C next down..
#7
I am looking at having a whole house surge protector added to our home.
Looking at the manual, is says put it on it's own breaker near the top/power feed.
I am not able to put the breaker near the top.. Only spot I got is mid way.... Am I going to take risk of breakers that are above it, and items below it will be protected?
Looking at the manual, is says put it on it's own breaker near the top/power feed.
I am not able to put the breaker near the top.. Only spot I got is mid way.... Am I going to take risk of breakers that are above it, and items below it will be protected?
What your whole house surge protector will do is the same thing that your plug-in surge protectors have been doing: Protecting your electronic devices from damage from current fluctuations. The difference is that it will do it earlier, more robustly, and for every device in your house - including your HVAC controls, your entertainment system, your security system, your refrigerator, etc. Everything.
All that said, I did mot see an instruction about panel location in the installation instructions* that I found for the Leviton 51110-001 Residential Panel Surge Protection Device. Do you have a different set of instructions?
*Note: This link will download the .pdf file of the installation instructions that I found.
I was surprised that I didn't find that, because it's a common instruction. It's also one that I've taken with a grain of salt over the years. I've installed these in every conceivable breaker position, from the end of the buses closest to the feeders to the end furthest away. All have performed as expected, and still are, even though the oldest of them has now been in service for nearly 10 years. I wouldn't worry about it, and I certainly wouldn't make any great effort to re-work a panel to move the device closer to the feeders.
One question: Is there a reason you're considering this remotely mounted protector over one that mounts directly to the ungrounded buses? The installation instructions are full of cautions about minimizing the length of the conductors. As I was reading that, I was thinking "Why not just buy the one that plugs into a double breaker space, and eliminate the resistance and induction concerns they're raising, plus save the cost of the two 30A breakers the call for?"
#8
This is the one I installed at my panel: SYC-120/240-T2: Sycom Surge Inc. - Home
Mounts right in a knockout. I attached the wires to the first two breakers. Maybe it works, maybe it doesn't. All I know is that I haven't had anything fried since it has been installed. I will also note that I have never had anything fried before it was installed.
Mounts right in a knockout. I attached the wires to the first two breakers. Maybe it works, maybe it doesn't. All I know is that I haven't had anything fried since it has been installed. I will also note that I have never had anything fried before it was installed.

#9
Nash,
I must of been out of it when I was reading the install manual... It was step #4 that I was looking at.
This unit can be mounted on the panel's knock out so the run is very short, and I already do have a spare 30 amp breaker.
I must of been out of it when I was reading the install manual... It was step #4 that I was looking at.
This unit can be mounted on the panel's knock out so the run is very short, and I already do have a spare 30 amp breaker.
#10
I must of been out of it when I was reading the install manual...

I already do have a spare 30 amp breaker.
#11
You need two single-pole 30A breakers, one above the other, IIRC. I would join their handles with a handle tie if I were doing it.
#12
You need two single-pole 30A breakers, one above the other, IIRC. I would join their handles with a handle tie if I were doing it.
#13
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Yes, Jay, that is correct. I am a bit surprised by the requirement for a 30 ampere breaker. As Joe mentioned, most manufacturers, at least the one's that I have come across, specify a 15 or 20 ampere circuit breaker.
#14
It's a 220v 30amp breaker that I have. Am sure that will work, right?
Originally Posted by Leviton 51110-001 Installation Instructions, Point 5
Leads from the SPD must be connected to the power mains through a 30 Amp (maximum) disconnect and fusing means. Either dedicated branch circuit breakers (independent single-pole preferred), or a fused disconnect switch may be used. [emphasis added]
And, as I said earlier,
Originally Posted by Nashkat1
I would join their handles with a handle tie if I were doing it.
Your call. I've told you the way I'd do it, for my own house or for a customer, and why.
#15
As Joe mentioned, most manufacturers, at least the one's that I have come across, specify a 15 or 20 ampere circuit breaker.
#17
If you were doing this, then both breaker will trip together then?
Both the two-pole breaker and the two tied-together individual breakers provide - ensure - simultaneous disconnect, but the two individual single-pole breakers can each trip without tripping the other half of the pair. That's why Leviton took pains to voice their preference for the two individual breakers in their instructions, and that's why I said that that's the method of disconnect I would install if I were doing the work.

#20
Thanks again, Nash!
One last question... Is there a reason why 220v breakers are on top? (like A/C, electric stove/dryers)
ONly 220v I got is the A/C, everything else is gas.. But in my past service days I've seen most of them on top.
A very very few case they are in the lower section or midway.
One last question... Is there a reason why 220v breakers are on top? (like A/C, electric stove/dryers)
ONly 220v I got is the A/C, everything else is gas.. But in my past service days I've seen most of them on top.
A very very few case they are in the lower section or midway.