SER cable into an exterior surface-mounted spa disconnect panel?

I'd like to install a packaged, surface-mount spa GFCI disconnect panel on the exterior of my recently-built stucco home.

The 40A circuit the builder installed for me is SER 6-6-6-6 down the interior of the wall to a 4" non-metallic box low in the wall, open to the exterior, currently capped with wire-nuts and covered with a weatherproof plate.

My thought was to pull the SER up to a new opening about 5' high, and bring it through the stucco and the rear knock-out of the surface-mounted disconnect panel. My question is, is there an NEC 2008-compliant way to secure and protect the SER, and maintain the weather-resistance of the box?

If not, any suggestions as to an alternative? The panel I'm looking at has conduit hub knock-outs on the top and bottom as well as the knock-out in the rear.

Thanks,
John
 
Sponsored Links
  #2  
Old 11-28-12, 07:50 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,361
You should be fine to use the knockout on the back of the disconnect. Add a SER clamp to the cable and secure with a locknut.

Add an upside down U of caulk above the cable.
 
  #3  
Old 11-28-12, 09:46 PM
Member
Thread Starter
Join Date: Jul 2008
Posts: 4
Great, thanks for the help!

John
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
'