I am trying to wire a dedicated circuit for my welder:

POWER MIGŪ 180C MIG Welder

I have been told I need to run 8/2 to a 3 Prong Plug. (NEMA Type 6-50P). 2 hot and 1 ground to a 40 amp breaker.

I would just like to run that by everyone here in case they see a potential problem with this setup?? Also, I have some 8/3 cable already - can I just use that and if so, should I use the extra wire as a ground as well or something or just cut it?

Thanks!
 
Sponsored Links
  #2  
Old 11-30-12, 09:30 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,659
What is the input amps? Neither your link or a couple others I checked give that. NEMA 6-50p is for a 50 amp circuit but you are talking about installing a 40 amp circuit.

It may be okay because of a low duty cycle but that is beyond my knowledge.
 
  #3  
Old 11-30-12, 10:02 AM
Member
Thread Starter
Join Date: Apr 2004
Location: Calgary, Canada
Posts: 382
Will upload the page from the manual.
 
  #4  
Old 11-30-12, 10:18 AM
Member
Thread Starter
Join Date: Apr 2004
Location: Calgary, Canada
Posts: 382
Here are the details from the manual.
 
Attached Images  
  #5  
Old 11-30-12, 10:36 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,659
Then you plan sounds good. If you use the 8-3 just cap the white at each end. You can not use it as an extra ground.
 
  #6  
Old 11-30-12, 06:51 PM
Member
Thread Starter
Join Date: Apr 2004
Location: Calgary, Canada
Posts: 382
Thanks for having a look for me....
 