Can I get away with 1" Flex Conduit with 8-10 pairs of #12 and 2 #10 ?
 
Sponsored Links
  #2  
Old 12-18-12, 11:23 AM
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 4,064
Fill-wise, that's probably fine... BUT, you can only have 9 current-carrying conductors in a raceway without derating the wiring. That means your 12ga wire will need to be connected to a 15A breaker and your 10ga to a 20A breaker.

You'd probably be better splitting them across two or more conduits. Also, don't forget about your ground!
 
  #3  
Old 12-18-12, 03:27 PM
Member
Thread Starter
Join Date: Jul 2009
Location: NYC
Posts: 302
Hmm...Thanks for the insight on the 9 Max.
I presume that's applicable to any gauge (regardless of fill capacity).

Yes, it's a flex run (5-6 feet) from transfer switch back to panel. The neutral and ground are the 10Awg. The remainder are 12AWG. Not that any of the circuits I am putting are nowhere even close to 20 draw. There's not even a microwave on that. The biggest draw would be the inrush from the fridge or the coffee maker.
 
  #4  
Old 12-18-12, 03:46 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
Sorry, but draw means nothing. Can you reduce the number of current-carrying conductors by having branch circuits share neutrals?
 
  #5  
Old 12-18-12, 05:18 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 11,990
Just a minor correction:

You are required to derate current carrying conductors if you have more than three wires in a raceway. However, the derateing does not really affect amp rateing of small conductors (as defined in the NEC) until more than 9 conductors is reached, so the info Nashkat providing is still true.
 

Last edited by Tolyn Ironhand; 12-18-12 at 05:46 PM.
  #6  
Old 12-18-12, 05:47 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
Point taken. Thanks for adding the detailed info, TI.
 
  #7  
Old 12-18-12, 06:10 PM
Member
Thread Starter
Join Date: Jul 2009
Location: NYC
Posts: 302
Interesting read fellas. I'm not using this but is this to say, they are using 12AWG but then breakers are 15amp - except for the last 2 which are 20...

31410B Pro/Tran | Product Details | Reliance Controls Corporation
 
  #8  
Old 12-19-12, 03:34 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 11,990
The key there is the whip is only 18" long. You do not have to take derateing into effect if the conduit is less than 24" long.
 
  #9  
Old 12-19-12, 03:50 AM
Member
Thread Starter
Join Date: Jul 2009
Location: NYC
Posts: 302
Got it. So I guess I'll end up running 2 conduits.

? For my Reference.
Is the neutral in the pipe considered a CC
 
  #10  
Old 12-19-12, 06:29 AM
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 4,064
If it's one neutral per hot, yes, it's a current-carrying conductor, since the voltage flows down the hot and back the neutral.

If you use two hots out of phase with a single neutral, the neutral is no longer considered current-carrying.

Grounds are never considered current-carrying, only figure into fill calculations.

------

Back to TI's comment, at what wire size does the 3 current carrying conductor derating limitation figure in? For small gauge wire (14/12/10), I know it's 9 current carrying conductors in a raceway, at what point does it decrease in number?

At some point I guess I'll have to break down and buy the NEC book and plan an exciting year to read it.
 
  #11  
Old 12-19-12, 08:04 AM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
What is the temperature rating of the conductors in that whip? I think those generator panels use either 105*c or 125*c rated wire.
 
  #12  
Old 12-19-12, 09:24 AM
Member
Thread Starter
Join Date: Jul 2009
Location: NYC
Posts: 302
I don't even have the slightest clue what they use in the whip.
I was just planning to use THNN 600V in my stash....

BTW, for 30 amps, the single #10 back should be sufficient right.
No benefit to go to a #8
 
  #13  
Old 12-19-12, 09:32 AM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
BTW, for 30 amps, the single #10 back should be sufficient right.
No benefit to go to a #8
Yes, 10 AWG is all you need for 30A.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
'