Can a GFCI fail without tripping the panel breaker?
Old 12-22-12, 10:21 AM
A GFCI-protected circuit in my garage has failed, but the panel breaker hasn't tripped and the GFCI reset latches. Is it possible that the GFCI has failed?
A plug in tester shows no lights.
If not, what else could account for a circuit failure in a 10-Yr old house?
There's no construction or other work being done that could have severed the hot.
Old 12-22-12, 10:30 AM
ray2047's Avatar
Breakers trip because of a short. GFCIs trip because of current leakage. Two very different things. Check all connections. If good replace the GFCI.
Old 12-22-12, 11:03 AM
Absolutely.....I change them out all the time. If you can set the GFI then you have power to it. If the receptacle is dead.... then the unit is defective.