Can I use 15A rate toggle switch on 20A circuit?

Reply

  #1  
Old 12-28-12, 05:17 PM
Member
Thread Starter
Join Date: Dec 2012
Location: usa
Posts: 2
Can I use 15A rate toggle switch on 20A circuit?

I an adding a couple of storage room lights to existing 20A circuit which gets no heavy loads. I noticed that my single pole toggle switch is rated 15A. Any problem using these?
In years past I never would have even paid attention but I live in a very rural part of Maine with little or no fire protection if a problem should occur. Thanks.
 
Sponsored Links
  #2  
Old 12-28-12, 08:21 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 11,991
As long as the connected load will never exceed the rateing of the switch, you may use a 15 amp switch on a 20 amp circuit.
 
  #3  
Old 12-29-12, 03:47 PM
Member
Thread Starter
Join Date: Dec 2012
Location: usa
Posts: 2
Thanks. Confirms my gut feeling but I feel better.
 