GFI Issue
#1
Member
Thread Starter
Join Date: Jun 2011
Location: USA
Posts: 53
Upvotes: 0
Received 0 Upvotes
on
0 Posts
GFI Issue
I have some of the GFI's in my house connected to a breaker in my box. My problem is I have 3 receptacles(2 in 1 bathroom & 1 in another that do not seem to be working). All other receptacles on that GFI breaker are all working.
I have tested & all 3 receptacles are live for power; however, nothing you plug into those 3 receptacles work as if no power is going to them.
Thoughts & thanks!!
I have tested & all 3 receptacles are live for power; however, nothing you plug into those 3 receptacles work as if no power is going to them.
Thoughts & thanks!!
#4
Group Moderator
No, I didn't ask whether you tested, as you already said that, what I asked was how you tested them.
#6
Some confusion here....
You say "some of the GFI's in my house connected to a breaker in my box" then you say "other receptacles on that GFI breaker".
Are they GFCI receptacles or regular receptacles connected to a GFCI breaker?
More than one GFCI on a circuit tends to not work.
Just clarifying.....
You say "some of the GFI's in my house connected to a breaker in my box" then you say "other receptacles on that GFI breaker".
Are they GFCI receptacles or regular receptacles connected to a GFCI breaker?
More than one GFCI on a circuit tends to not work.
Just clarifying.....
#11
What you should do is buy an analog voltmeter or multimeter. The kind with the needle. $10-15 at most places that sell them.
The light up testers aren't always accurate.
It's very odd that you have a GFCI breaker unless this is a newer home. Most times they just used a GFCI receptacle as the first in line which protected all the others.
Are you sure all these receptacles are on the same circuit? Where are the working ones located? By room I mean.
It could be that the first non-functional one has a loose wire, or the last functional one does. Relatively simple to check and figure out how they run.
If you don't feel comfortable removing them from the wall and checking, then yes, you'll need to call a Pro.
The light up testers aren't always accurate.
It's very odd that you have a GFCI breaker unless this is a newer home. Most times they just used a GFCI receptacle as the first in line which protected all the others.
Are you sure all these receptacles are on the same circuit? Where are the working ones located? By room I mean.
It could be that the first non-functional one has a loose wire, or the last functional one does. Relatively simple to check and figure out how they run.
If you don't feel comfortable removing them from the wall and checking, then yes, you'll need to call a Pro.
#12
Group Moderator
Do you have access to a multi-meter? I don't think the test you did to show power was valid, we need to know more specific information.
Edit: Looks like Vic types faster than I do
Edit: Looks like Vic types faster than I do

#15
The other receptacles are located in the bathroom downstairs(works) & in the kitchen(both are working)
You should use either an analog multimeter or a GFCI receptacle tester to test these receptacles.
#16
Member
Thread Starter
Join Date: Jun 2011
Location: USA
Posts: 53
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks to everyone...problem solved..there was power to all the receptacles involved. I just followed Gunguy45's advice & followed the circuit.
I cut the power to the circuit & at the first non-functioning receptacle was a loose connection. Repaired it, turned the circuit back on & bingo all the receptacles after that were ok.
Don't know what I'd do without these forums.
You guys are a huge help.
Thanks again.
I cut the power to the circuit & at the first non-functioning receptacle was a loose connection. Repaired it, turned the circuit back on & bingo all the receptacles after that were ok.
Don't know what I'd do without these forums.
You guys are a huge help.
Thanks again.
#17
Group Moderator
Glad you got it working and thanks for the update, we don't hear how things work often enough around here.