AC Breaker tripping


  #1  
Old 01-24-13, 03:58 PM
J
Member
Thread Starter
Join Date: Jan 2013
Location: USA
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
AC Breaker tripping

In my main panel (200 amp) I have a 100 amp breaker that feeds a sub panel for my two AC unit's aux power. They are 60 amp breakers for each of the Aux units. When it is very cold and both ACs are on and require the Aux coils it will frequently trip the sub panel 100 amp breaker in my main panel.

If the wire from the main to the sub is #4 or bigger can I change out the 100 amp breaker for a 125 amp breaker?

My panel and breakers are Gould/ I-T-E brands.

Thanks
 
  #2  
Old 01-24-13, 05:24 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
95a is max foe #4 even at the 90° listing. Even less at the 60° rating which may apply in this case depending on the rating of the connections. First you need to check the actual amp draw with a clamp on amp meter. It could just be a weak breaker.
 
  #3  
Old 01-24-13, 05:24 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,842
Received 179 Upvotes on 162 Posts
First of all, A-C units don't normally run in the winter. It sounds as if you have two heat pumps with 10 KW auxiliary electric strip heat for each one. The 100 amp breaker should probably be changed to 125 amps, but the feeder must be big enough for 125 amps.

If the wire from the main to the sub is #4 or bigger can I change out the 100 amp breaker for a 125 amp breaker?
No, you cannot change from 100 to a 125 amp breaker if the feeder is a #4. A #4 copper conductor can be used as a residential 100 amp feeder, but that's actually more than the conductor is rated for. You'll need a minimum size of #2 copper or 1/0 aluminum for a 125 amp residential feeder. My opinion is based upon an assumption that you have 10 KW auxiliary electric strip heat with each heat pump, you need to verify exactly what you have.
 
  #4  
Old 01-24-13, 06:50 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,157
Received 814 Upvotes on 685 Posts
I think you would be better off running a new 60 amp feed off the 200 amp panel and re-feeding one of the heat pumps. Getting one of the 60 amp loads off the 100 amp panel will solve your problem, and be cheaper to install.
 
 