grounding a subpanel

I am building a barn (24' X 32') and will be installing a subpanel (likely 60A). If I understand correctly NEC 2008 requires a separate grounding for the subpanel for which I plan to run the appropriate gauge wire to a ground rod. I will be installing a lightning protection system with two ground rods. My question is: can I ground my subpanel to the lightning protection system ground rod? Seems like it should not be a problem, as any lightning strike will go to ground, not to the subpanel. Thanks.
 
  #2  
Old 02-02-13, 01:11 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
You need a separate ground wire (EGC) back to the supplying panel to provide a low resistance path for clearing faults. Ground rods are for a totally different purpose (GEC) and you need those also for a detached structure.
 
  #3  
Old 02-02-13, 01:20 PM
Y
Member
Thread Starter
Join Date: Feb 2013
Location: USA
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for you quick reply. I plan to run a 4-wire cable (2 hots, neutral & ground) from the main panel (house) to the subpanel in the barn. My question is whether I can use my lightning protection ground rod as my GEC for the subpanel, or do I need a separate ground rod.
 
  #4  
Old 02-02-13, 03:55 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
Not only can you use the grounding electrodes for the lightening protection for the panel grounding electrode you MUST tie all grounding electrodes together (electrically) for a proper installation.
 
  #5  
Old 02-03-13, 09:48 AM
Y
Member
Thread Starter
Join Date: Feb 2013
Location: USA
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks Furd. My lightning protection system will have 2 10' ground rods driven 4-6' out from the foundation at either end of the barn, all connected. As long as I run my subpanel ground wire to one of those rods, it will be part of the system. I presume this will work.
 
  #6  
Old 02-03-13, 11:26 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
Use nothing smaller than #6 solid copper for the grounding electrode conductor (GEC)and connect it to the ground rod with an acorn clamp below the surface of the ground. Bury the copper GEC.
 
  #7  
Old 02-03-13, 02:55 PM
Y
Member
Thread Starter
Join Date: Feb 2013
Location: USA
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Will do - thanks again for the help.
 
 