120v generator: transfer switch need help
hello. newbie here and need some help. I have a briggs & stratton 30320 4k running/5k starting generator that has 4 20 amp duplex outlets, no 240v. I wanted to install a transfer switch in the house that would power a few 120v circuits i.e. furnace, fridge, lights. I want to install a inlet box on outside the house for convenience. The only problem i am finding is that the kit i want is a reliance 3006hdk transfer switch wich includes 30 amp transfer switch and 6 circuits. I would like this kit so that when i do buy a larger generator with a 240v it would power 4 120v and 1 240v circuits. But for now, I was thinking I could only connect 1 leg of the transfer switch to my 120v generator and power the 3 120v circuits in the house. Couple of questions:
1.Can i just power 1 leg of the transfer switch without causing damage to my generator or fuse panel/appliances?
2. How would i wire the 30 amp l14-30 inlet to my 5-20 120v generator?
3. Is it possible to just run 1 hot and 1 neutral to the l14-30 from the 5-20 120v on generator so it sends 120v to the transfer switch?
Thanks for your assistance. I have looked online for answers for weeks without getting a definite answer.
Marco
1.Can i just power 1 leg of the transfer switch without causing damage to my generator or fuse panel/appliances?
2. How would i wire the 30 amp l14-30 inlet to my 5-20 120v generator?
3. Is it possible to just run 1 hot and 1 neutral to the l14-30 from the 5-20 120v on generator so it sends 120v to the transfer switch?
Thanks for your assistance. I have looked online for answers for weeks without getting a definite answer.
Marco
#2
You cant do it with that gen. Just run cords as you normally are. With that gen each duplex is running off a winding. If you run on one side winding only then the gen becomes unbalanced.......
What is your 240v circuit you want to run?
What is your 240v circuit you want to run?
#5
I would forget about the a/c. You will need a large gen for that.
Heat, re-fridge, lights, water...etc are more important. Smaller gen uses less fuel. Being in NJ I could tell you how hard it was to find gas for 9 days during sandy....... I only went through some 15 gallons.
Spend your money wisely.....
Heat, re-fridge, lights, water...etc are more important. Smaller gen uses less fuel. Being in NJ I could tell you how hard it was to find gas for 9 days during sandy....... I only went through some 15 gallons.
Spend your money wisely.....
#7
Plug the light refridge on one side duplex with ext cords.
Get a transfer switch for your funace and plug iy into the other duplex.
TF201W Easy/Tran | Product Details | Reliance Controls Corporation
If you really want to not run ext cords then you will need two of these. Plug a cord from each duplex into each transfer switch. Each transfer switch will power on side of your panel with 4 circuits per side. But are all only 15 amp. They will need to be wired properly.
Remember cant run 240 loads
15114A Pro/Tran | Product Details | Reliance Controls Corporation
But why spend that money????? By a new 120/240 gen and a 120/240 transfer switch.
Note your gen will produce only 2000 watts per side of the panel. And I do not know of the codes involved so wait for the electricians.
You know I am a plumber right??????
Get a transfer switch for your funace and plug iy into the other duplex.
TF201W Easy/Tran | Product Details | Reliance Controls Corporation
If you really want to not run ext cords then you will need two of these. Plug a cord from each duplex into each transfer switch. Each transfer switch will power on side of your panel with 4 circuits per side. But are all only 15 amp. They will need to be wired properly.
Remember cant run 240 loads
15114A Pro/Tran | Product Details | Reliance Controls Corporation
But why spend that money????? By a new 120/240 gen and a 120/240 transfer switch.
Note your gen will produce only 2000 watts per side of the panel. And I do not know of the codes involved so wait for the electricians.
You know I am a plumber right??????
#8
Member
Thread Starter
Join Date: Feb 2013
Location: Usa
Posts: 7
Received 0 Votes
on
0 Posts
So, the problem with this generator is that it has 4 duplex outlets and the load has to be balanced across them. I just got an email from generator direct and they said i could use the reliance 30114a with my 30320 generator. Is that correct?
#9
Member
Thread Starter
Join Date: Feb 2013
Location: Usa
Posts: 7
Received 0 Votes
on
0 Posts
I was told i can use something called an adapt y to create 240v and that will enable me to balance the load. ADAPT-Y Generator Cord Adaptor
Sorry for all the questions, but keep getting different answers. Can you clarify if this adapt y would work? Thanks again
Sorry for all the questions, but keep getting different answers. Can you clarify if this adapt y would work? Thanks again
#10
yes the 30114a. But you will only be drawing from one winding on the gen and limited to 2000 watts. Plus the gen will be un balanced if drawing from one side. It will rock and roll if you draw max power and probably break.....
#11
Member
Thread Starter
Join Date: Feb 2013
Location: Usa
Posts: 7
Received 0 Votes
on
0 Posts
So what about that adapt y ? ADAPT-Y Generator Cord Adaptor would that balance the loads across the Two sets of duplex?
#12
No that adapter will only work if the neutral and ground are bonded. And if they are bonded then you will have the whole issue of bonding/transfer switch issues.
And infact that cord is a suicide cord IMO. If one end became un plugged could it be live and dangerous???
And infact that cord is a suicide cord IMO. If one end became un plugged could it be live and dangerous???