what could be wrong with the wiring of this GFCI?
#1
Member
Thread Starter
Join Date: Feb 2013
Location: United States
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
what could be wrong with the wiring of this GFCI?
In a washroom, I have two outlets - one a GFCI and the other normal two plug receptacle. When I connect say a shaver to the GFCI - it's fine. When I connect to the plug, it trips the GFCI outlet.
I replaced the plug with a new one thinking a faulty plug could be the cause. It made no difference.
Opened the GFCI outlet and I see one white wire going from the line side to a marette with a bunch of other white wires, a hot/black wire from the load side but no white wire from the load side.
On the plug side, I only see a black/hot
and a white wire (and a ground wire) connected properly.
I turned off at the breaker panel and did not find any other receptacles that turned off. The lights and the fan in the washroom continue to work. So it does not seem to be feeding any other outlets or devices.
I have attached photos of the two plugs. Any suggestions?

Greatly appreciate your help.
I replaced the plug with a new one thinking a faulty plug could be the cause. It made no difference.
Opened the GFCI outlet and I see one white wire going from the line side to a marette with a bunch of other white wires, a hot/black wire from the load side but no white wire from the load side.
On the plug side, I only see a black/hot
and a white wire (and a ground wire) connected properly.
I turned off at the breaker panel and did not find any other receptacles that turned off. The lights and the fan in the washroom continue to work. So it does not seem to be feeding any other outlets or devices.
I have attached photos of the two plugs. Any suggestions?


Greatly appreciate your help.
#2
It's tripping because of how the neutrals are connected. You need to find the neutral for the "load", the single receptacle, and place it into the correct position on the GFCI.
The GFCI looks for a balance in the current in the hot/neutral lines. The way it is wired, it can't do that. The hot line to the receptacle is drawing current (and being measured) but the GFCI is bypassed on the neutral side (not measured). It thinks there's a ground fault.
Instant trip. The GFCI is working correctly.
The GFCI looks for a balance in the current in the hot/neutral lines. The way it is wired, it can't do that. The hot line to the receptacle is drawing current (and being measured) but the GFCI is bypassed on the neutral side (not measured). It thinks there's a ground fault.
Instant trip. The GFCI is working correctly.
#3
Member
Thread Starter
Join Date: Feb 2013
Location: United States
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks aandpdan,
Any suggestions on how to isolate the neutral feeding the load/receptacle in the washroom from the ones that are all twisted up..
After identifying the neutral that feeds the receptacle in the washroom, what do I do with the rest neutrals - leave them as they are?
thanks
Any suggestions on how to isolate the neutral feeding the load/receptacle in the washroom from the ones that are all twisted up..
After identifying the neutral that feeds the receptacle in the washroom, what do I do with the rest neutrals - leave them as they are?
thanks
#4
Any suggestions on how to isolate the neutral feeding the load/receptacle in the washroom from the ones that are all twisted up.
what do I do with the rest neutrals
#5
Do you have an ohmmeter ?
Turn off power to that circuit
You will need to open the white splice.
You will have 3 whites and the jumper to the GFI.
Using your ohmmeter set to Rx1 check from the white wire on the single outlet to the three white wires. One will show continuity.
That wire goes to the neutral (white) side of the GFI on the terminal UNDER that yellow label.
Put the other three white wires back together.
That should do it.
Turn off power to that circuit
You will need to open the white splice.
You will have 3 whites and the jumper to the GFI.
Using your ohmmeter set to Rx1 check from the white wire on the single outlet to the three white wires. One will show continuity.
That wire goes to the neutral (white) side of the GFI on the terminal UNDER that yellow label.
Put the other three white wires back together.
That should do it.
#6
Member
Thread Starter
Join Date: Feb 2013
Location: United States
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks Nashkat1
The panel has a separate breaker for just the washroom - which means these two receptacles (one with gfi and the other without) nothing else should be downstream from this gfi.
So, I think wiring the neutrals off the line side of the gfi should be ok.
thanks for your feedback.
The panel has a separate breaker for just the washroom - which means these two receptacles (one with gfi and the other without) nothing else should be downstream from this gfi.
So, I think wiring the neutrals off the line side of the gfi should be ok.
thanks for your feedback.
#7
Member
Thread Starter
Join Date: Feb 2013
Location: United States
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
thanks PJmax
Nope, I don't have any meters, except for the little tester that buzzez if the wire is live..
But I understand exactly what you said - basically I need to match the wire coming from the single outlet to the piglet of white wire and determine which is the other end of it...that end then goes to the white side of the load connector on the gfi.
And the rest of the wires remain the same.
What is interesting is that with the little tester (and the circuit breaker on the panel in off) I still get buzzing or light coming on on both the gfi and the single outlet..where could the juice be coming from?
Nope, I don't have any meters, except for the little tester that buzzez if the wire is live..
But I understand exactly what you said - basically I need to match the wire coming from the single outlet to the piglet of white wire and determine which is the other end of it...that end then goes to the white side of the load connector on the gfi.
And the rest of the wires remain the same.
What is interesting is that with the little tester (and the circuit breaker on the panel in off) I still get buzzing or light coming on on both the gfi and the single outlet..where could the juice be coming from?
#8
I don't have any meters, except for the little tester that buzzez if the wire is live.

#10
Thanks Nashkat1
The panel has a separate breaker for just the washroom - which means these two receptacles (one with gfi and the other without) nothing else should be downstream from this gfi.
So, I think wiring the neutrals off the line side of the gfi should be ok.
thanks for your feedback.
The panel has a separate breaker for just the washroom - which means these two receptacles (one with gfi and the other without) nothing else should be downstream from this gfi.
So, I think wiring the neutrals off the line side of the gfi should be ok.
thanks for your feedback.
#11
Member
Thread Starter
Join Date: Feb 2013
Location: United States
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ok, got everything to work...method of elimination....we found the pair coming from the single outlet and did exactly what PJmax suggested.
Manually trip the gfi and the single outlet is off
All the tests pass.
thanks everyone...
Manually trip the gfi and the single outlet is off
All the tests pass.
thanks everyone...
#12
Member
Thread Starter
Join Date: Feb 2013
Location: United States
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
thanks JerseyMatt,
That's exactly what we ended up doing.
The trick was in finding the right neutral that was feeding the second outlet...with just the circut buzzer tester...I should really be buying an analog tester as suggested by ray2047.
With the power on the panel to on, we just tested all the neutrals and when we found an inactive one - that was the likely candidate...then we tested and of course it was the only one..
More tests and we nailed it...
Must say...my first time on this forum and very impressive with the quality of assistance/advise...thanks everyone.
That's exactly what we ended up doing.
The trick was in finding the right neutral that was feeding the second outlet...with just the circut buzzer tester...I should really be buying an analog tester as suggested by ray2047.
With the power on the panel to on, we just tested all the neutrals and when we found an inactive one - that was the likely candidate...then we tested and of course it was the only one..
More tests and we nailed it...
Must say...my first time on this forum and very impressive with the quality of assistance/advise...thanks everyone.