Wiring for hot tub


  #1  
Old 02-20-13, 12:30 PM
B
Member
Thread Starter
Join Date: Feb 2013
Location: CANADA
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Wiring for hot tub

I need to know if I can run 6/3 romex cable from my panel to my hot tub. The tub is around 150 ft away from the panel and is an interior application. The tub although rated for 60 amps, the manufacturer says it draws max 54amps with all pumps running. Will the 6/3 with the loss factor be sufficient enough or do I have to upgrade to 4/3 romex. I will be installing a GFCI 10' away from the tub making the lenght of the run to around 140'..
 
  #2  
Old 02-20-13, 01:40 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 7,458
Upvotes: 0
Received 5 Upvotes on 4 Posts
Welcome to the forums!

The voltage drop calculator I used gave me #2 copper for 300' for a 120V circuit, or #6 copper for 150' for a 240V circuit.

The length of the run is 150'. You need the 54 amps at the tub, not at the disconnect.
 
  #3  
Old 02-20-13, 03:55 PM
B
Member
Thread Starter
Join Date: Feb 2013
Location: CANADA
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
the voltage will be 240V/60 amps max. Is it OK to go with a 3% Voltage drop over this lenght of 150'
 
  #4  
Old 02-20-13, 05:31 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 7,458
Upvotes: 0
Received 5 Upvotes on 4 Posts
Yes. Anything less than 3% is considered an acceptable result. Appliances are supposed to be designed to operate with voltage that is within 10%, each way, of their labeled voltage. That's 216V to 264V for your hot tub.

It's not the best practice to go to either edge of that range, of course. But ~233V, if that's what you wind up with, should be OK.
 
  #5  
Old 02-21-13, 11:40 AM
D
Member
Join Date: Apr 2002
Location: USA
Posts: 175
Upvotes: 0
Received 0 Upvotes on 0 Posts
National electrical code requires that the wiring for hot tubs consist of a GREEN insulated ground wire of equal size to the other wires. ROMEX has a bare copper wire, one size smaller than the other wires. Hence, it would be a violating of code to use romex to wire a hot tub.

Mod Note: the grounding conductor can be bare for the interior wiring portion of the circuit.
 

Last edited by pcboss; 02-23-13 at 02:07 PM.
  #6  
Old 02-21-13, 01:01 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 7,458
Upvotes: 0
Received 5 Upvotes on 4 Posts
National electrical code requires that the wiring for hot tubs consist of a GREEN insulated ground wire of equal size to the other wires. ROMEX has a bare copper wire, one size smaller than the other wires. Hence, it would be a violating of code to use romex to wire a hot tub.
Things may have changed. From the 2011 NEC (emphasis added):
680.21 Motors.
(A) Wiring Methods.
The wiring to a pool motor shall comply
with (A)(1) unless modified for specific circumstances by
(A)(2), (A)(3), (A)(4), or (A)(5)....

(4) One-Family Dwellings. In the interior of dwelling units,
or in the interior of accessory buildings associated with a
dwelling unit, any of the wiring methods recognized in Chapter
3 of this Code that comply with the provisions of this
section shall be permitted. Where run in a cable assembly, the
equipment grounding conductor shall be permitted to be uninsulated
,
but it shall be enclosed within the outer sheath of the
cable assembly.
In the Romex[SUP]®[/SUP] sold now, the EGC is the same size as the other conductors.
 
  #7  
Old 02-23-13, 06:59 AM
B
Member
Thread Starter
Join Date: Feb 2013
Location: CANADA
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the input. Does the code change apply for Ontario/Canada or is that US only.
 
  #8  
Old 02-23-13, 09:37 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
No code applies locally except local code. National codes are guidelines only unless adopted in whole without amendments by local authorities having jurisdiction. CEC can vary from NEC which is what was referenced. Bottom line the only opinion that counts is the local inspector's opinion. Ask him to be sure. Also note there are differences sometimes between US and Canadian NM-b cable.
 
  #9  
Old 02-23-13, 02:08 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,937
Received 181 Upvotes on 159 Posts
The code quoted by Nash is from the NEC.
 
  #10  
Old 02-23-13, 08:33 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Dr. Spa do you have a NEC cite for the grounding conductor size? Even in conduit using insulated wire it is code to use #10 for the EGC on a 60a circuit. Is there an exception in the NEC for Spas?
 
 