Dead Outlet
I have half an outlet that is not working. The bottom of the outlet has the garbage disposal plugged in, the upper outlet has the dishwasher plugged in. There is no power to the dishwasher, but the disposal is working fine. I plugged the dishwasher into another outlet and it work. Why would one side of a duplex outlet stop working. I have reset the c/b on the dishwasher and reset all of the GFI outlets. No joy...........any solutions.
#2
Welcome to the forums.
That receptacle may have had it's hot side bridge clip broken off so that two circuits could utilize one receptacle.
Do you know if the disposal and dishwasher are on two different circuits ?
That receptacle may have had it's hot side bridge clip broken off so that two circuits could utilize one receptacle.
Do you know if the disposal and dishwasher are on two different circuits ?
#3
You have a split receptacle...the GD is controlled by a switch right? The DW side would be hot all the time.
You have different feeds to each side. You may find that they have been wired using the backstab holes on the back. Very common for those to fail.
You'll need to pull the outlet out and tell us what you find.
You have different feeds to each side. You may find that they have been wired using the backstab holes on the back. Very common for those to fail.
You'll need to pull the outlet out and tell us what you find.
#5
Is it just a matter of replacing the outlet???
#8
Turn the garbage disposal on and let it run with water running through it, then turn on the dishwasher. Does the dishwasher come on? If so, the receptacle was wired completely through the switch, improperly.