Receptacles dead after breaker tripped & reset
#1
Member
Thread Starter
Join Date: Mar 2013
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Receptacles dead after breaker tripped & reset
I had a breaker trip after overloading a circuit. After resetting the breaker all of the receptacles on the circuit have no power. I checked all of the CGFIs in the house and none are tripped.
What next?
Thanks
What next?
Thanks
#2
Welcome to the forums.
On that circuit......is ANY receptacle working ?
If no.....you'll need to check breaker for output first.
If that is ok..... you'll need to go to the closest receptacle (that's on that circuit) to the panel to see if that is live.
On that circuit......is ANY receptacle working ?
If no.....you'll need to check breaker for output first.
If that is ok..... you'll need to go to the closest receptacle (that's on that circuit) to the panel to see if that is live.
#6
Oops! Found the culprit. A GFCI that was hidden and I didn't know existed. It was tripped.
Sorry for taking up your time on something so simple.
Sorry for taking up your time on something so simple.