I've read that flexible conduit needs to be supported every 4 1/ 2 feet and within 12 inches on each side of every outlet box or fitting. If I have a span greater that that distance what is the best method of providing horizontal support?

Specifically I have florescent light fixtures hanging from steel beam roof supports with flex conduit running between them. The distance between lights is around 8'. At one point there was a drop ceiling and I'm guessing the flex was just sitting on top the ceiling tiles, but all that has been removed and the conduit between lights is just hanging in air.
 
  #2  
Old 03-19-13, 08:08 AM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 7,458
Upvotes: 0
Received 5 Upvotes on 4 Posts
The flex cable should have been supported by being attached to separate steel wires that were attached to the overhead steel and the ceiling grid - but did not support the ceiling grip - when that was in place.

The wiring for an open ceiling should be run on the building structure and follow a support wire down to each fixture.

If the fixtures that are hanging now are 2X4 lay-in fixtures, they are probably not rated for use as hanging fixture.
 
  #3  
Old 03-19-13, 08:15 AM
E
Member
Thread Starter
Join Date: Jul 2007
Location: ohio usa
Posts: 141
Upvotes: 0
Received 0 Upvotes on 0 Posts
I'll check the fixtures to see if they are rated for hanging.

The conduit might be a problem as the roof is support by steel beams with insulation under them. There doesn't appear to be any easy method of dropping wires every 3.5' to support the conduit.

Could threaded rod be dropped vertically, say every 10-12' and then some sort of horizontal run be put in place to support the flex?
 
  #4  
Old 03-20-13, 01:58 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 7,458
Upvotes: 0
Received 5 Upvotes on 4 Posts
The conduit might be a problem as the roof is support by steel beams with insulation under them.
When you stand in this space and look up you can only see insulation? None of the roof support system is visible?

Some pictures might help us see what you have. See How To Put Pictures In Your Post.

There doesn't appear to be any easy method of dropping wires every 3.5' to support the conduit.
Not that it makes a lot of difference, but Is it conduit with individual conductors pulled through it or is it metal-sheathed cable? More to the point, what are the fixtures suspended from?

No one has suggested that you drop wires to support the cables or conduit. What I suggested was that
Originally Posted by Nashkat1
The wiring for an open ceiling should be run on the building structure and follow a support wire down to each fixture.
That is, the wiring should be run overhead and be attached to one of the existing fixture support wires between the building structure and each fixture.

Could threaded rod be dropped vertically, say every 10-12' and then some sort of horizontal run be put in place to support the flex?
Yes. You would need to use 1-1/2" uni-strut or a similar product, mounted with the open face toward the floor. It will need to be made continuous with splice plates and supported at intervals no greater than 10'. Both the fixtures and the wiring will need to be attached to the support strut assembly.

The best work platform for this work is a scissors lift. It will be a lot easier with a helper. I would start by setting up a couple of work lights on stands and demoing all of the existing lighting. Unless it is is modern lighting with electronic ballasts and T-8 lamps, this would be the ideal time to upgrade it.

What will the all-thread be mounted to?
 
  #5  
Old 03-20-13, 03:26 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,151
Received 809 Upvotes on 682 Posts
As Nashkat posted, upload a picture of what your working with and we could suggest fittings that you can use. There are a great deal of fittings and products that are used to connect all sorts of hangers to beams and the like. I am sure we could come up with something.

I would also suggest using MC cable or similar for wiring lights.
 
  #6  
Old 03-20-13, 05:51 PM
E
Member
Thread Starter
Join Date: Jul 2007
Location: ohio usa
Posts: 141
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks guys, I'll be able to get some pictures this weekend and look to get a better idea of the existing.
 
  #7  
Old 03-20-13, 07:50 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,933
Received 180 Upvotes on 158 Posts
This sounds like it might be a commercial space. If so the OP may need a licensed contractor to do the work.
 
 