Supporting conduit
#1
Member
Thread Starter
Join Date: Jul 2007
Location: ohio usa
Posts: 141
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Supporting conduit
I've read that flexible conduit needs to be supported every 4 1/ 2 feet and within 12 inches on each side of every outlet box or fitting. If I have a span greater that that distance what is the best method of providing horizontal support?
Specifically I have florescent light fixtures hanging from steel beam roof supports with flex conduit running between them. The distance between lights is around 8'. At one point there was a drop ceiling and I'm guessing the flex was just sitting on top the ceiling tiles, but all that has been removed and the conduit between lights is just hanging in air.
Specifically I have florescent light fixtures hanging from steel beam roof supports with flex conduit running between them. The distance between lights is around 8'. At one point there was a drop ceiling and I'm guessing the flex was just sitting on top the ceiling tiles, but all that has been removed and the conduit between lights is just hanging in air.
#2
The flex cable should have been supported by being attached to separate steel wires that were attached to the overhead steel and the ceiling grid - but did not support the ceiling grip - when that was in place.
The wiring for an open ceiling should be run on the building structure and follow a support wire down to each fixture.
If the fixtures that are hanging now are 2X4 lay-in fixtures, they are probably not rated for use as hanging fixture.
The wiring for an open ceiling should be run on the building structure and follow a support wire down to each fixture.
If the fixtures that are hanging now are 2X4 lay-in fixtures, they are probably not rated for use as hanging fixture.
#3
Member
Thread Starter
Join Date: Jul 2007
Location: ohio usa
Posts: 141
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I'll check the fixtures to see if they are rated for hanging.
The conduit might be a problem as the roof is support by steel beams with insulation under them. There doesn't appear to be any easy method of dropping wires every 3.5' to support the conduit.
Could threaded rod be dropped vertically, say every 10-12' and then some sort of horizontal run be put in place to support the flex?
The conduit might be a problem as the roof is support by steel beams with insulation under them. There doesn't appear to be any easy method of dropping wires every 3.5' to support the conduit.
Could threaded rod be dropped vertically, say every 10-12' and then some sort of horizontal run be put in place to support the flex?
#4
The conduit might be a problem as the roof is support by steel beams with insulation under them.
Some pictures might help us see what you have. See How To Put Pictures In Your Post.
There doesn't appear to be any easy method of dropping wires every 3.5' to support the conduit.
No one has suggested that you drop wires to support the cables or conduit. What I suggested was that
Originally Posted by Nashkat1
The wiring for an open ceiling should be run on the building structure and follow a support wire down to each fixture.
Could threaded rod be dropped vertically, say every 10-12' and then some sort of horizontal run be put in place to support the flex?
The best work platform for this work is a scissors lift. It will be a lot easier with a helper. I would start by setting up a couple of work lights on stands and demoing all of the existing lighting. Unless it is is modern lighting with electronic ballasts and T-8 lamps, this would be the ideal time to upgrade it.
What will the all-thread be mounted to?
#5
As Nashkat posted, upload a picture of what your working with and we could suggest fittings that you can use. There are a great deal of fittings and products that are used to connect all sorts of hangers to beams and the like. I am sure we could come up with something.
I would also suggest using MC cable or similar for wiring lights.
I would also suggest using MC cable or similar for wiring lights.
#7
This sounds like it might be a commercial space. If so the OP may need a licensed contractor to do the work.