Wiring for outdoor kitchen
#1
Member
Thread Starter
Join Date: Nov 2001
Location: Washington State
Posts: 86
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Wiring for outdoor kitchen
installing an outdoor kitchen with an overhead pergola. The kitchen island will have three standard 110V/15 amp gfi outlets in series. The overhead pergola will have an infrared heater: 220V/18.1 amp/4000W load. The wiring run from the panel to the patio is about 100 ft. I believe i need 12 awg wire for the outlets and 14 awg for the heater. Does that look correct?
Also -- I plan on using direct bury wiring on this project. Any problem running direct buried through a metal conduit up onto the pergola?
Thanks,
Also -- I plan on using direct bury wiring on this project. Any problem running direct buried through a metal conduit up onto the pergola?
Thanks,
#2
The 4kw heater that will be running on 240 vac will draw approx 17 amps. On a continuous draw device.....you can not exceed 80% of the breaker rating which means 16 amps continuous load. You may have to run # 10 wire to it.
electric heater helpful hints sizing chart.pdf
The receptacles would probably be best on a 20 amp circuit which would mean #12 wiring. You could use one GFI receptacle to protect all three locations.
electric heater helpful hints sizing chart.pdf
The receptacles would probably be best on a 20 amp circuit which would mean #12 wiring. You could use one GFI receptacle to protect all three locations.
#3
he kitchen island will have three standard 110V/15 amp gfi outlets in series.
Last edited by ray2047; 03-19-13 at 03:56 PM.
#4
Member
Join Date: Mar 2013
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
You will need minimum 12AWG to the heater, which I'm assuming is a 220V- only heater. In that case, you can run 12-2 with the neutral taped Red or Black. (My $0.02: Tape it red, because it will make the breaker look like it is running double pole, and makes it look a little bit more professional, in my opinion.) You do not need more than 1 GFCI, and I believe that you should have, by the NEC 2011, it be a 20amp receptacle, that is if it is on or above the countertop.
Sparky
Sparky
#5
I believe that you should have, by the NEC 2011, it be a 20amp receptacle, that is if it is on or above the countertop.
#6
The kitchen island will have three standard 110V/15 amp gfi outlets in series. The overhead pergola will have an infrared heater: 220V/18.1 amp/4000W load.
#7
You will need minimum 12AWG to the heater, which I'm assuming is a 220V- only heater.