Help - Fluorescent shop light tripping GFCI

I have a plug in style 4' fluorescent shop light 2-Light 48" White High Performance Fluorescent Plug In Shoplight at Menards that trips my Leviton GFCI receptacle when I try to turn it on. I replaced an older GFCI with the Leviton, the older one did not trip. I tried a different plug in fluorescent and did not have any issues either. I replaced the receptacle so I could get a GFCI with a light on it, as it also powers my sump pump, making it easier to see if it's tripped or not.

Do I have a defective light? GFCI? Or are the two simply not agreeing with each other?

Thank you for your thoughts.
 
  #2  
Old 03-23-13, 08:32 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,456
Received 1,416 Votes on 1,310 Posts
It is very likely that the ballast has a leak to ground. If they fixture is new get it exchanged.
If not....you can get a replacement ballast for it.
 
  #3  
Old 03-24-13, 11:50 AM
M
Member
Thread Starter
Join Date: Jun 2012
Location: USA
Posts: 71
Received 0 Votes on 0 Posts
Thanks PJ - I tried a replacement and it worked just fine, that was likely the problem!
 
 