outdoor wire

Reply

  #1  
Old 03-25-13, 05:17 PM
Member
Thread Starter
Join Date: Mar 2013
Location: United States
Posts: 2
outdoor wire

I am adding an outdoor box and connecting it to another outdoor box. I ran out of 12-2g, but found some 14-3-g. Can I/should I splice the two in order to finish the run of about 15 feet?
thanks
 
Sponsored Links
  #2  
Old 03-25-13, 05:19 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,631
No, if this is on a 20 amp breaker.
 
  #3  
Old 03-25-13, 05:58 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,212
These are outdoor boxes, is the wiring being run outdoors too?
 
  #4  
Old 03-25-13, 08:24 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
Sounds like you're working with cable. What kind of cable are you using? Are you running it in conduit? Is it buried?
 
  #5  
Old 03-26-13, 01:55 PM
Member
Thread Starter
Join Date: Mar 2013
Location: United States
Posts: 2
nm-b, buried, started with 12-2g found some extra 14-3g connecting to another exterior box.
 
  #6  
Old 03-26-13, 03:22 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
nm-b, buried, started with 12-2g found some extra 14-3g connecting to another exterior box.
Type NM is only rated for use inside closed spaces in the interior. It is not rated for use outdoors, not rated for direct burial, and not rated for installation in conduit.

You need to use a different wiring method.

Reading a copy of Wiring Simplified would probably answer a lot of questions for you.
 