Properly wiring a GFCI Breaker in a Subpanel
#1
Member
Thread Starter
Join Date: Mar 2013
Posts: 17
Received 0 Votes
on
0 Posts
Properly wiring a GFCI Breaker in a Subpanel
I'm building an Electrical Brewery so I need to protect myself from any mishaps. The current setup has the Neutral bar and the ground bar common. I believe to properly wire a GFCI Breaker the Neutral bar must be isolated from the ground bar and enclosure. Where I currently have all the neutral/white wires I don't think i can isolate that bar. So I'll need to isolate the small ground bar in the upper right corner and run the white wires to that and then run all the bare copper wires where the white wires are now. Please advise if i'm correct or what else I need to do. I've attached pictures of the sub-panel, GFCI and the isolation kit. The actual GFCI breaker I'm installing is a DP 20A HOM220GFI and will replace the DP 20A std breaker on the right.
Edit, crap I can't be right with above. The neutral wire from my feeder is on the neutral bar now. How do I isolate the neutral bar? if i put the grounds there i can't accomplish what I want. I don't know how to set up this panel.
Edit, crap I can't be right with above. The neutral wire from my feeder is on the neutral bar now. How do I isolate the neutral bar? if i put the grounds there i can't accomplish what I want. I don't know how to set up this panel.
#2
Welcome to the forums!
Isolated neutrals and bonded grounds are not necessary for GFCI breakers to work properly. They work just fine in common-bonded main distribution panels.
You need to isolate the neutrals because this is a subpanel. Remove any ground wires from the bar that the feeder neutral is connected to and test for continuity between that bar and the box. If you find continuity, look for the screw or strap that is bonding them together, remove it, and test again. Once you have that bar isolated, connect the neutrals to it and the grounds to the small bar in the upper right corner.
Thank you for the pictures. Why are you installing a 2-pole 240V GFCI breaker? What will it be protecting?
See above. It may already be isolated.
I believe to properly wire a GFCI Breaker the Neutral bar must be isolated from the ground bar and enclosure.
Where I currently have all the neutral/white wires I don't think i can isolate that bar. So I'll need to isolate the small ground bar in the upper right corner and run the white wires to that and then run all the bare copper wires where the white wires are now. Please advise if i'm correct or what else I need to do.
I've attached pictures of the sub-panel, GFCI and the isolation kit. The actual GFCI breaker I'm installing is a DP 20A HOM220GFI and will replace the DP 20A std breaker on the right.
The neutral wire from my feeder is on the neutral bar now. How do I isolate the neutral bar?
#3
I believe to properly wire a GFCI Breaker the Neutral bar must be isolated from the ground bar and enclosure.
So I'll need to isolate the small ground bar in the upper right corner and run the white wires to that
How do I isolate the neutral bar?
The above assumes that is a subpanel. If it isn't the answers change.
Echo... echo.
#4
Edit, crap I can't be right with above. The neutral wire from my feeder is on the neutral bar now. How do I isolate the neutral bar? if i put the grounds there i can't accomplish what I want. I don't know how to set up this panel.
#5
Member
Thread Starter
Join Date: Mar 2013
Posts: 17
Received 0 Votes
on
0 Posts
I can't find any grounding screw or Bonding screw. The one screw on the far right of the Neutral bar has a strange head and I'm assuming that it's not supposed to be removed. It's not allen, hex, phillips or square. It looks to be hex but it is so shallow I can't get anything to grip it or seat properly to remove it. The one bare wire that looks like it's in the Neutral bar isn't, it comes out of the sheathing and rounds it's way to the ground bar in the upper right corner.
The Neutral bar has continuity to the box/ground bar. The third hole left from the right end of the Neu bar has nothing in it. But it looks like I can see all the way through to the plywood that the panel is mounted on. Don't know the function of this hole. I can see the panel has a factory hump on the back of the panel from that hole. Like maybe it would be where it would be grounded to the panel.
The Neutral bar has continuity to the box/ground bar. The third hole left from the right end of the Neu bar has nothing in it. But it looks like I can see all the way through to the plywood that the panel is mounted on. Don't know the function of this hole. I can see the panel has a factory hump on the back of the panel from that hole. Like maybe it would be where it would be grounded to the panel.
#6
On your neutral bar, the third hole from the right, there is no screw, right? That is where your bonding screw would go if it were a primary panel. You will find that green screw in a plastic bag inside the panel somewhere. Don't use it and the neutral bar is isolated.
#7
Member
Thread Starter
Join Date: Mar 2013
Posts: 17
Received 0 Votes
on
0 Posts
Hi Chandler
Yup the third hole from the right is empty but the Neutral Bar is still common with the panel. When I put my meter on logic the neutral bar beeps when shorting the panel or the ground bar. There are only white neutral wires from the attached breakers in the neutral bar. Could the total continuity be coming from my main panel in the basement. I had an electrician put a 40A breaker in my QO panel in the basement to supply power to this homeline sub panel in my garage. I tend to think not. would no mater what I had, i should be able to isolate the neutral bar from the panel.
BTW my 40A breaker in the basement is off so I don't get any surprises.
Yup the third hole from the right is empty but the Neutral Bar is still common with the panel. When I put my meter on logic the neutral bar beeps when shorting the panel or the ground bar. There are only white neutral wires from the attached breakers in the neutral bar. Could the total continuity be coming from my main panel in the basement. I had an electrician put a 40A breaker in my QO panel in the basement to supply power to this homeline sub panel in my garage. I tend to think not. would no mater what I had, i should be able to isolate the neutral bar from the panel.
BTW my 40A breaker in the basement is off so I don't get any surprises.
#10
Member
Thread Starter
Join Date: Mar 2013
Posts: 17
Received 0 Votes
on
0 Posts
OK were getting somewhere, not sure where but my logic beeper is finally silent. First I took all the breaker white wires out and it still had continuity. So I took out the large white wire from the basement breaker and now I can experience Isolation from the panel.
So what does this tell me? Do I just swap out the std 20A breaker and put in the GFCI 20A breaker and it's good to go or do I need to do something in the basement?
I think the coiled up white wire goes to the neutral bar and the white wire that goes to the 20A 240v receptacle goes to the GFCI breaker instead of the neutral bar. Please don't holler too loud if I'm wrong I'm an old man and I might faint. LOL
So what does this tell me? Do I just swap out the std 20A breaker and put in the GFCI 20A breaker and it's good to go or do I need to do something in the basement?
I think the coiled up white wire goes to the neutral bar and the white wire that goes to the 20A 240v receptacle goes to the GFCI breaker instead of the neutral bar. Please don't holler too loud if I'm wrong I'm an old man and I might faint. LOL
#11
I think the coiled up white wire goes to the neutral bar and the white wire that goes to the 20A 240v receptacle goes to the GFCI breaker instead of the neutral bar.

#14
I take it that it doesn't matter that the panel and the neutral bar will read common because of the wiring from the basement QO panel?
I don't need to do anything else?

But I'm still curious.
Originally Posted by Nashkat1
Why are you installing a 2-pole 240V GFCI breaker? What will it be protecting?
#15
Member
Thread Starter
Join Date: Mar 2013
Posts: 17
Received 0 Votes
on
0 Posts
Oh crap,
Now what? When this breaker was originally wired up the white wire wasn't supposed to coil around and into the bottom of the breaker but only a short jaunt over and down into the Neutral bar.
My white wire isn't long enough for the journey. It's in a conduit that has tooo many twists to allow any pulling of the wire through the conduit. is there anyway I can splice about 12" on the end of the white wire to loop around to the bottom of the GFCI Breaker?

Now what? When this breaker was originally wired up the white wire wasn't supposed to coil around and into the bottom of the breaker but only a short jaunt over and down into the Neutral bar.

#16
is there anyway I can splice about 12" on the end of the white wire to loop around to the bottom of the GFCI Breaker?

Are you going to answer my question about the 2-pole breaker?
#17
Member
Thread Starter
Join Date: Mar 2013
Posts: 17
Received 0 Votes
on
0 Posts
But I'm still curious.
Quote Originally Posted by Nashkat1
Why are you installing a 2-pole 240V GFCI breaker? What will it be protecting?
Read more: http://www.doityourself.com/forum/ne...#ixzz2PB5bpSGt
Quote Originally Posted by Nashkat1
Why are you installing a 2-pole 240V GFCI breaker? What will it be protecting?
Read more: http://www.doityourself.com/forum/ne...#ixzz2PB5bpSGt
I'm building an Electric Beer Brewing Panel that will control two 3500 Watt water heater elements in both the Boil Kettle and the Hot Liquor Tank via PID's and RTD temperature probes. Also two food grade liquid pumps, pump the hot liquids to various vessels. It's common practice and normal procedure to protect these panels (ie, me) due to the liquids involved.
They heavily stress the GFCI protection in their instructions.
Electric Brewery
Last edited by Clare Valley; 03-31-13 at 08:39 PM.
#19
Member
Thread Starter
Join Date: Mar 2013
Posts: 17
Received 0 Votes
on
0 Posts
is there anyway I can splice about 12" on the end of the white wire to loop around to the bottom of the GFCI Breaker?
Sure. Just use wire the same gauge.
Sure. Just use wire the same gauge.
#22
What's the best procedure for splicing the wires?
#23
Member
Thread Starter
Join Date: Mar 2013
Posts: 17
Received 0 Votes
on
0 Posts
and that panel needs to be supplied with 240V power?
If it was 120V 20A the max is 2000w, still not enough.
240V 20A can power 3500w and with 6 gal it will work and boil the wort.
Most of the panel builders use 20gal kettles and make 10 to 12 gal batches and they use 240V 30A to power 5500w elements.
120V just isn't enough power to boil the wort sufficiently. If it would boil the wort it would be too slow and that isn't good as air contaminants would have too much time to take hold and leave off flavors.
Use pliers to twist the wires together with at least three twists, clockwise. Trim the end if needed. Hand-twist a wire nut on to protect the splice.
You can see the plans for the panel here
Thanks for all your help and sorry I missed the question from earlier.
#24
240V 20A can power 3500w and with 6 gal it will work and boil the wort.
My 12 GA wire is stranded from the bulk rolls at Lowes. Will that present any problems splicing with the solid 12 GA wire?
#25
Member
Thread Starter
Join Date: Mar 2013
Posts: 17
Received 0 Votes
on
0 Posts
It should be fine. I spread stranded conductors into a brush shape, lay that next to ant solid conductors and just twist a wire nut on when I need to splice those together.