Question exposed romex

I am running 2 new circuits to my upstairs bathroom using my pantry downstairs and the linen closet upstairs as a pathway to the attic. The space has been used to run other utilities to the attic from the basement, i.e., central vac line, and HVAC lines. I plan to secure the romex to one of these pipes. Is that ok or does the romex have to be enclosed? if so, can I use a wire channel?
 
  #2  
Old 03-29-13, 07:40 AM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,675
Received 178 Votes on 159 Posts
Code states that NM-B (Romex) needs to be protected when it's in an area 'subject to damage'. In the back of a closet, in my opinion, it would be subject to things being leaned on it, boxes, etc.

But it's a pretty easy fix. You can sleeve the NM-B in gray PVC conduit, then attach the conduit to the wall with conduit straps. A 3/4" conduit can handle sleeving two 12 or 14ga NM-B cables without a problem. You don't need to do anything special at the top and bottom of each conduit.
 
  #3  
Old 03-29-13, 08:50 AM
B
New Member
Thread Starter
Join Date: Feb 2002
Location: USA
Posts: 18
Received 0 Votes on 0 Posts
Thanks Mike...I had heard you shouldn't run romex inside conduit; it had to be separate strand wire. Not sure why. To me that would require a splice box at each end to connect the romex back into the circuit.
Thanks again.
 
  #4  
Old 03-29-13, 09:00 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,581
Received 13 Votes on 11 Posts
It is best practice not to run cable in a complete conduit system but it is common, even recommended, to sleeve cable with conduit to protect it.
 
 