Shed wiring project + generator
I'm planning to wire my shed this spring. I've done a lot of reading, so I think I have most of my plan put together. I'd like to see if there's anything I'm doing that is not appropriate, or could be better.
Details:
The shed is 100' from the house
Wiring will leave the house 50' from the main panel
I plan to run 50A service to the shed for future use (potentially a pool)
Short term will only be used for lights and minor 120V shop appliances (compressor, table saw, chop saw, etc.)
Inside:
50A DP breaker on the main panel
6/3 NM-B to the exterior wall
Connections made in LB body at house
Outside:
1" schedule 40 PVC, buried >= 18" deep
3x 6AWG THHN in the conduit *
1x 10AWG Green THHN in the conduit (GND)
*Can all 3 be black marked with Red/White markings on the ends of two of them? My local supply shops don't sell Red/White by the foot.
Second 1" conduit for CAT5e/RG-6... why not if I'm already digging...
Shed:
Sub-panel with 50A main breaker
2x 8' GND rods, likely buried at 45 degree angle due to bedrock
GND rods connected by uninsulated #4
Generator:
If I want to hook up the generator in the shed, is there any way to do this?
Details:
The shed is 100' from the house
Wiring will leave the house 50' from the main panel
I plan to run 50A service to the shed for future use (potentially a pool)
Short term will only be used for lights and minor 120V shop appliances (compressor, table saw, chop saw, etc.)
Inside:
50A DP breaker on the main panel
6/3 NM-B to the exterior wall
Connections made in LB body at house
Outside:
1" schedule 40 PVC, buried >= 18" deep
3x 6AWG THHN in the conduit *
1x 10AWG Green THHN in the conduit (GND)
*Can all 3 be black marked with Red/White markings on the ends of two of them? My local supply shops don't sell Red/White by the foot.
Second 1" conduit for CAT5e/RG-6... why not if I'm already digging...
Shed:
Sub-panel with 50A main breaker
2x 8' GND rods, likely buried at 45 degree angle due to bedrock
GND rods connected by uninsulated #4
Generator:
If I want to hook up the generator in the shed, is there any way to do this?
#2
Connections made in LB body at house
Can all 3 be black marked with Red/White markings on the ends of two of them?
Sub-panel with 50A main breaker
Generator:
If I want to hook up the generator in the shed, is there any way to do this?
If I want to hook up the generator in the shed, is there any way to do this?
#3
Member
Thread Starter
Join Date: Mar 2013
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Best to use a 4x4 junction box so you have room the connections. Some conduit bodies do not have the cubic inches stamped in and can't therefor by code be use for connections. Doubt the cubic inces even if marked would be enough.
#6 and smaller can't be redesignated white. You don't need a red and black. Two blacks are fine.
Does not need to be a 50 amp breaker. Would suggest a 100 amp main breaker panel so you have enough spaces. The 100 amp breaker that comes with it is fine because it is only used as a disconnect. You will need to buy and install a ground bar.
Is that to power the shed only?
#4
If it were #8, redesignated would be OK? Seems illogical...
Thanks. Ground bar needs to remain isolated from neutral, correct?
I can't think of a way to use the shed feed for a generator. Maybe the pros can, Simplest is a second set of wires.
#5
Inside:
50A DP breaker on the main panel
6/3 NM-B to the exterior wall
50A DP breaker on the main panel
6/3 NM-B to the exterior wall
The good news:
In pipe #6 Cu is good for 60A with a #10 ground and 70A with a #8 ground.
With enough 240V loads, the neutral does not need to be bigger than the ground.
#6
Connections made in LB body at house
Outside:
1" schedule 40 PVC, buried >= 18" deep
1" schedule 40 PVC, buried >= 18" deep
3x 6AWG THHN in the conduit *
1x 10AWG Green THHN in the conduit (GND)
1x 10AWG Green THHN in the conduit (GND)
GND rods connected by uninsulated #4
Generator:
If I want to hook up the generator in the shed, is there any way to do this?
If I want to hook up the generator in the shed, is there any way to do this?
Last edited by Glennsparky; 03-29-13 at 11:54 PM.
#7
... The ground must be copper...
#8
The shed is 100' from the house
Wiring will leave the house 50' from the main panel
Wiring will leave the house 50' from the main panel
Second 1" conduit for CAT5e/RG-6... why not if I'm already digging...
Originally Posted by Glennsparky
A pool's feed must be piped the whole way... The '11 code decided that sch 80 was not sufficient for a physical damage location for pools. Only rigid (RMC) or intermediate (IMC) are allowed. You can still convert to sch 40 below 18" depth. 680.25(A)(1)
#9
Member
Thread Starter
Join Date: Mar 2013
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Alright, so far, my takeaways:
1 - Generator needs to be it's own wires back. Two questions:
a - Does it need it's own neutral? GND?
b - Is it necessary for it to be in it's own conduit?
2 - The schedule 40 is OK as it's going to the shed. Future run to pool from shed would need to be RMC/IMC.
3 - THWN - got it. Was planning on this anyway. Home Depot wire calls itself THHN, but it's really THHN/THWN-2.
4 - Can't redesignate as white unless I bump up to #4 wire (may not be a bad idea for voltage drop anyway.
Now, a few more questions:
If I were go to what I consider the opposite extreme, and decide to only run 20A on a GFCI (screw the pool & generator):
1 - I only need to bury to 6", no conduit if UF-B, correct?
2 - Is there anything against putting it in a conduit anyway?
3 - Can I run as big a wire as I want (eg. #6), as long as the breaker in my main panel is 20A, GFCI?
4 - Can I run two sets of wires (eg. 2x 6/2) so I have 2x120V (not 220V), or does that bring me back to being 18" and conduit?
1 - Generator needs to be it's own wires back. Two questions:
a - Does it need it's own neutral? GND?
b - Is it necessary for it to be in it's own conduit?
Third 1" conduit for the feed from the generator to the house...
It sounds like you're just feeding the subpanel with this run, and that you'll feed the pool equipment from the subpanel. If so, then the special requirements for the wiring methods for pools should only apply as yor install that run; i.e., from the subpanel to the pool.
4 - Can't redesignate as white unless I bump up to #4 wire (may not be a bad idea for voltage drop anyway.
Now, a few more questions:
If I were go to what I consider the opposite extreme, and decide to only run 20A on a GFCI (screw the pool & generator):
1 - I only need to bury to 6", no conduit if UF-B, correct?
2 - Is there anything against putting it in a conduit anyway?
3 - Can I run as big a wire as I want (eg. #6), as long as the breaker in my main panel is 20A, GFCI?
4 - Can I run two sets of wires (eg. 2x 6/2) so I have 2x120V (not 220V), or does that bring me back to being 18" and conduit?
#10
a - Does it need it's own neutral? GND?
b - Is it necessary for it to be in it's own conduit?
1 - I only need to bury to 6", no conduit if UF-B, correct?
2 - Is there anything against putting it in a conduit anyway?
3 - Can I run as big a wire as I want (eg. #6), as long as the breaker in my main panel is 20A, GFCI?x
Can I run two sets of wires (eg. 2x 6/2) so I have 2x120V (not 220V), or does that bring me back to being 18" and conduit?
#11
Member
Thread Starter
Join Date: Mar 2013
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ray -
Thanks for all the answers, again!
I was unclear in one (possibly many, but you sifted through it), so let me ask a different way:
What are the limitations to when I only need to bury the cable 12" deep?
I understand that it needs to be GFCI protected, and I would go with UF-B direct burial. Am I only allowed a 120V/20A (max) circuit, or could I run 220/240V, 20A.
Thanks for all the answers, again!
I was unclear in one (possibly many, but you sifted through it), so let me ask a different way:
What are the limitations to when I only need to bury the cable 12" deep?
I understand that it needs to be GFCI protected, and I would go with UF-B direct burial. Am I only allowed a 120V/20A (max) circuit, or could I run 220/240V, 20A.
#12
Am I only allowed a 120V/20A (max) circuit, or could I run 220/240V, 20A.
Originally Posted by ray2047
You could run a multiwire circuit that would give you two 120v 20 amp circuits. You would need red, black, white, ground... The multi wire counts as one branch circuit. It would be connected to a 20a 240 breaker or two handle tied 120v 20a breakers on opposite legs of the 240.
#13
Member
Thread Starter
Join Date: Mar 2013
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
In looking at the 2011 NEC, Table 300.5 Column 4 is:
Although I would love to be able to run the multi-wire, this is why I was hesitant.
Residential Branch Circuits Rated 120 Volts or Less with GFCI Protection and Maximum Overcurrent Protection of 20 Amperes
#14
What are you trying to power? A multiwire 20A branch circuit is a 20A 240V circuit, plus a neutral, or it's two 20A 120V circuits. It just can't be both. 
List the loads you need to power and we can come up with the service needed.

List the loads you need to power and we can come up with the service needed.
#15
Member
Thread Starter
Join Date: Mar 2013
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Nashkat -
I don't have a good definition of what loads - but likely just various tools/radio, and some lighting.
My recent question was because I would like to maximize the power/effort ratio. If I'm digging a 110', 12" trench and I can only run 120V/20A, so be it. If I can run twice as much power at the same depth (effort), I will.
Going to 18" will be an issue with roots, rocks, etc. that I'd like to avoid. It also adds the additional work/cost of a conduit, unless I go to 24", which will be even more roots, rocks, etc.
So, my question still stands (but I think 300.5 answered it): Is 120V/20A with GFCI breaker the max I can run at a depth of 12" (putting aside RMC/IMC), or is a multi-wire config still compliant to code?
I don't have a good definition of what loads - but likely just various tools/radio, and some lighting.
My recent question was because I would like to maximize the power/effort ratio. If I'm digging a 110', 12" trench and I can only run 120V/20A, so be it. If I can run twice as much power at the same depth (effort), I will.
Going to 18" will be an issue with roots, rocks, etc. that I'd like to avoid. It also adds the additional work/cost of a conduit, unless I go to 24", which will be even more roots, rocks, etc.
So, my question still stands (but I think 300.5 answered it): Is 120V/20A with GFCI breaker the max I can run at a depth of 12" (putting aside RMC/IMC), or is a multi-wire config still compliant to code?
#16
Yes, that is the way I read table 300.5(2008).
I always use a Sawzall with a 12" wrecking blade when I dig. Doesn't do a thing for rocks but sure goes through roots. You can actually stick it in the gound and cut a path for you digging.
I always use a Sawzall with a 12" wrecking blade when I dig. Doesn't do a thing for rocks but sure goes through roots. You can actually stick it in the gound and cut a path for you digging.
#17
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Without getting my code book out and looking up the referenced article I am going to state that a multi-wire branch circuit supplied through a two-pole, 20 ampere GFCI circuit breaker may indeed be laid in a trench with only 12 inches of cover. In almost all cases when the code states a voltage it is voltage to ground and a 240 volt circuit still is only 120 volts TO GROUND.
#18
Going to 18" will be an issue with roots, rocks, etc. that I'd like to avoid. It also adds the additional work/cost of a conduit, unless I go to 24", which will be even more roots, rocks, etc.
I don't have a good definition of what loads - but likely just various tools/radio, and some lighting.
My recent question was because I would like to maximize the power/effort ratio.
My recent question was because I would like to maximize the power/effort ratio.
If you don't need any 240V power in the shed, the GFCI-protected cable you're thinking of burying can be used for a multiwire branch circuit. Just make it 12-3/G Type UF.
#19
Member
Thread Starter
Join Date: Mar 2013
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yes, that is the way I read table 300.5(2008).
Without getting my code book out and looking up the referenced article I am going to state that a multi-wire branch circuit supplied through a two-pole, 20 ampere GFCI circuit breaker may indeed be laid in a trench with only 12 inches of cover. In almost all cases when the code states a voltage it is voltage to ground and a 240 volt circuit still is only 120 volts TO GROUND
If you don't need any 240V power in the shed, the GFCI-protected cable you're thinking of burying can be used for a multiwire branch circuit. Just make it 12-3/G Type UF.
With my configuration of a multi-wire branch circuit, what are the grounding requirements for the shed? Does it still require 2 ground rods, etc. or was that only when I was bringing larger service and a sub-panel?
#20
The additional grounding at the shed is for a subpanel; you won't need that with the multiwire circuit.
The better way to protect the two circuits is with two single-pole breakers with their handles connected with a handle tie.
Pretty heavy wire. I hope it'll fit onto your breakers and devices. How long is the run?
a multi-wire branch circuit with a 20A double-pole GFCI breaker
I'll be getting 8/3 UF, only because of the length of the run and voltage drop.
#21
I don't necessarily agree or disagree with Furd. I see it as basically a 240 volt circuit that is split into two 120 circuits at the shed. I don't know on further thought.
If you go with a multiwire circuit all you need is a disconnect. Cheapest way may be to use an unfused AC disconnect or you can install a box and 2-pole 20a switch (DPST).
If you go with a multiwire circuit all you need is a disconnect. Cheapest way may be to use an unfused AC disconnect or you can install a box and 2-pole 20a switch (DPST).
#22
Member
Thread Starter
Join Date: Mar 2013
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The better way to protect the two circuits is with two single-pole breakers with their handles connected with a handle tie.
Pretty heavy wire. I hope it'll fit onto your breakers and devices. How long is the run
If you go with a multiwire circuit all you need is a disconnect. Cheapest way may be to use an unfused AC disconnect or you can install a box and 2-pole 20a switch (DPST).
Leviton 20 Amp Commercial Double-Pole Toggle Switch
#23
Member
Thread Starter
Join Date: Mar 2013
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I hope it'll fit onto your breakers and devices.
#24
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
I dug out my 2002 NEC and read Article 300.5 and looked at the table. Then I looked up "voltage" under Article 100 (Definitions) where the term voltage is further broken down to Voltage of a circuit; Voltage, nominal and Voltage to Ground. Voltage of a circuit is defined as "The greatest root-mean-square (rms) (effective) difference of potential between any two conductors of the circuit concerned."
That along with Table 300.5 column 4 that states in part, "...120 volts or less with GFCI protection..." now tells me that a multi-wire branch circuit is NOT acceptable in any manner detailed in column 4. That leaves you to going back to 18 inch minimum depth or using one of the other methods listed in Table 300.5.
That along with Table 300.5 column 4 that states in part, "...120 volts or less with GFCI protection..." now tells me that a multi-wire branch circuit is NOT acceptable in any manner detailed in column 4. That leaves you to going back to 18 inch minimum depth or using one of the other methods listed in Table 300.5.
#25
Member
Thread Starter
Join Date: Mar 2013
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Furd -
Thanks for diving in. If I start digging and it's "uneventful", maybe I'll change the plan, but given the # of rocks I hit while digging the footings for the shed itself I'm likely going with 120V/20A.
Thanks to all for the help!
Thanks for diving in. If I start digging and it's "uneventful", maybe I'll change the plan, but given the # of rocks I hit while digging the footings for the shed itself I'm likely going with 120V/20A.
Thanks to all for the help!