Splicing 12 gauge to 14 gauge on 15 amps
#1
Member
Thread Starter
Join Date: Mar 2013
Location: usa
Posts: 28
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Splicing 12 gauge to 14 gauge on 15 amps
Hi All.
Can I splice 12/2 and 14/2 (on a 15 amp breaker). The breaker is the 14/2 side.
The 12/2 comes from a bathroom fan which I can't access to replace with a full run of 14/2.
Thanks
Can I splice 12/2 and 14/2 (on a 15 amp breaker). The breaker is the 14/2 side.
The 12/2 comes from a bathroom fan which I can't access to replace with a full run of 14/2.
Thanks
#3
Member
Join Date: Mar 2013
Location: USA
Posts: 27
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I learn something new every day. For example: I thought you could run 12-2 to a GFCI and 14-2 on the protected end of the GFCI but not the other way around. I have done a lot of extra work for nothing.
#4
Forum Topic Moderator
smithdavidp, just to clarify...
You can use 14ga or anything larger (12ga, 10ga, etc) wire on a circuit protected by a 15A breaker. You can NOT use 14ga wire on a 20A breaker anywhere in the circuit.
So if you used 12ga to the first GFI and 14ga from there on out, the circuit must be protected by a 15A breaker.
You can use 14ga or anything larger (12ga, 10ga, etc) wire on a circuit protected by a 15A breaker. You can NOT use 14ga wire on a 20A breaker anywhere in the circuit.
So if you used 12ga to the first GFI and 14ga from there on out, the circuit must be protected by a 15A breaker.
#6
15amp breaker to a GFCI using 12 and then 14 for the protected end which has two lights
#7
Member
Join Date: Mar 2013
Location: USA
Posts: 27
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The GFCI is in the garage. Code says that all accessible circuits must be GFCI protected and that all light switches must have a ground. Having the lights on the GFCI prevents hazardous shocks from possible contact with the metal screws holding the wall plate in place.
Would you please state the code that requires 20 amp circuit breakers in a sub panel. The panel has been inspected and approved by the county electrical inspector.
Would you please state the code that requires 20 amp circuit breakers in a sub panel. The panel has been inspected and approved by the county electrical inspector.
#8
Would you please state the code that requires 20 amp circuit breakers in a sub panel.
Nashkat1 said:
In a kitchen or bathroom, it needs to be on a 20A circuit.
#9
The GFCI is in the garage. Code says that all accessible circuits must be GFCI protected and that all light switches must have a ground. Having the lights on the GFCI prevents hazardous shocks from possible contact with the metal screws holding the wall plate in place.
Originally Posted by 2011 NEC Article 210.8
All 125-volt, single-phase, 15- and 20-ampere receptacles installed in... (2) Garages,
Having the lights on the GFCI prevents hazardous shocks from possible contact with the metal screws holding the wall plate in place.
#10
Member
Join Date: Mar 2013
Location: USA
Posts: 27
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Code states that sub panels can not have the neutral bonded to the case. The main panel is the only panel that can have the bonding screw installed. I started a topic :Is #8 wire overkill for a 40 amp panel. All the folks that answered were greatly concerned that I had, in fact, installed the bonding screw. It was, however, a trick of the light which made a silver colored screw look green. Evidently I misread the code thinking that it stated circuits and not just receptacles. In any case the inspector said there was nothing wrong with protecting the light circuits but he felt that it was a little overboard as far as my safety concerns go so you are absolutely correct on that count.