adding surge protecter
#1
adding surge protecter
Since I live in the lightning capital of the world, (central Florida) I have a 10 year old surge protector on my main panel outside the house. This main panel has additional ckt breakers that feed two rooms in the house. The remainder of the house is feed from the main panel to a 200A panel in the garage. The garage panel feeds the heat pump and goes thru a disconnect panel on the outside wall by the heat pump. I want to install an additional surge protector there and had decided on a "Supco SCM150". Just completed a service call on the heat pump 2 weeks ago ($500) fryed ckt board, #1 wondering if this is a problem with 2 surge protectors? #2 the ground rod is back at the main panel, should I drive a new ground rod @ the disconnect panel also? Tx
Last edited by pcboss; 04-09-13 at 06:28 PM.
#2
There is no problem with a second surge suppressor, in fact, it's a good idea for supplemental protection if you are having problems, but I am wondering about the integrity of the 10 year old surge suppressor at your main panel? Does it have indicating lights to show if it is still effective and operating correctly? The ground rod at your main panel is sufficient if it meets the 25 ohm or less resistance requirement. If in doubt, add a second ground rod at least 6 feet away from the first ground rod. Keep in mind that damaging surges can and do originate within your home too and not always do they come from lightning.
#3
Yes the original surge protector still has lights showing. I was going to replace that one as well just because of the age. Interesting connection, the main surge protector is connected thru dedicated circuit breakers to the main buss. The new surge protector shows connection directly to the buss, no circuit breakers there except the ones in the garage. I used to use a megger back in the day to check the ground rod, don't have one now and I am not about to disconnect the connection to the ground rod to measure.
Wonder if the power company would do a "complimentary" check, probably not since they sell the surge protectors and then charge you $6 a month. Tx...

#4
the main surge protector is connected thru dedicated circuit breakers to the main buss. The new surge protector shows connection directly to the buss, no circuit breakers there except the ones in the garage.
#5
Hope I can clarify. The main panel (outside) has space in it for 10 breakers. As previously stated, some of these breakers feed 2 rooms in the house. The remaining breakers, 1 for the sprinkler system and 2 breakers for the surge protector. (2 black wires from the surge to breakers that bridge both sides of the main buss, white wire to neutral bar). 2 other breakers feed the hot tub. The new surge protector, (yet to be installed) is connecting to a disconnect box for my heat pump. (this connection comes from the garage panel)
#6
Tried to add photo to last post, retrying
Schematic show's connection to the heat pump side of the disconnect box at the same point where the wires run to the heat pump. I have ckt breakers in the garage panel, not in the disconnect.

#9
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
That's an interesting setup. I've never seen a surge protector wired to the overcurrent protection device that supplies the load.
There seems to be no neutral so where is the neutral connected and are those lugs rated for two wires.
#10
Tx for the great info. Got the new surge in the mail today and installed it. (Green light ON
) Looks like it hangs out from the wall about 7/8". Should I put a piece of PT wood or something behind to brace it. Seems pretty solid?
An added note from the manufacturer. "Although the SCM150 can be installed at the main breaker panel, SUPCO recommends installation at the service disconnect for the A/C condenser"

An added note from the manufacturer. "Although the SCM150 can be installed at the main breaker panel, SUPCO recommends installation at the service disconnect for the A/C condenser"
#12
I have seen them, paid little attention to them, but seems like a great idea. Its 7/8", probably go with a 3/4 and a washer or 2.
OOps The surge has a threaded shaft that you stick thru the hole and screw on a jam nut. Do they have a female offset nipple and a male side?. Ones I see on line look like male/male.?? (outside thread)
OOps The surge has a threaded shaft that you stick thru the hole and screw on a jam nut. Do they have a female offset nipple and a male side?. Ones I see on line look like male/male.?? (outside thread)