Electrical Subpanel in attic
#1
Member
Thread Starter
Join Date: Apr 2013
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Electrical Subpanel in attic
I want to put a subpanel (220v) in my attic to drop circuits to a remodeled kitchen. Plenty of clearence left and right and in front of the panel but attic is only 4' tall.
Per NEC; 110.26 (E) I need 6.5' clear headroom unless:
In existing dwelling units, service equipment or panelboards that do not exceed 200 amperes shall be permitted in spaces where the headroom is less than 2.0 m (6 1/ 2 ft).
House is existing, so am I ok with those clearences?
Per NEC; 110.26 (E) I need 6.5' clear headroom unless:
In existing dwelling units, service equipment or panelboards that do not exceed 200 amperes shall be permitted in spaces where the headroom is less than 2.0 m (6 1/ 2 ft).
House is existing, so am I ok with those clearences?
#4
Member
Join Date: Mar 2013
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I believe you are good to go with a panel less than 200A. Of course the code inspectors interpretation of that exception is the one that matters. Don't install it there and say "Ed said it was ok"

#5
Welcome to the forums!
Make a sketch of the location and take it with you when you file for the permit. Then you'll know whether they're willing to approve your proposal and the conditions you will have to meet to pass final.
Make a sketch of the location and take it with you when you file for the permit. Then you'll know whether they're willing to approve your proposal and the conditions you will have to meet to pass final.