Pool pump circuit.
Hi. Straight to it. I just had my fence replaced, and the contractor broke the conduit for the pool timer which sliced through the wire shrouds and caused a bunch of fireworks! Now I'm rewiring it and bringing it up to code....(I think). The issues I'm having are as follows: my understanding is that there must be a direct power source from panel to pump with only a gfci outlet and a switch allowed between. So far so good. I have a 1.24 hp pump, 12/3 wire to the gfci, 12g extension wire from gfci to a 20amp double pole switch and on to timer. The neutral from the 12/3 connected to the LINE side of the gfci but no neutral after that. (Perhaps I could run one from the LOAD side but to what?) 12/3 black to LINE, extension cord black from LOAD to LINE at the switch. 12/3 red is pigtailed to extension cord red and connected to LINE at the switch. GFCI keeps tripping.
#2
12/3 wire to the gfci, 12g extension wire from gfci to a 20amp double pole switch and on to timer.
#4
Service cord is not code compliant. You must use individual conductors in conduit. Romex can not be used outside even in conduit under any circumstances. Your local code may also require RMC instead of PVC for the conduit from the house to the pool.
#6
First replace the wiring with correct wiring and we can work on your problem if it still exists. Given though how dangerous pool wiring can be if done wrong and your lack of basic knowledge I would suggest hiring an electrician experienced in pool wiring.
#7
Member
Thread Starter
Join Date: Apr 2013
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I got it fixed. Replaced the romex with the correct wires, wired in gfci with tails so the gfci won't effect the switch or pump. Also had to add a sub-panel and upgrade the breakers to two double polled 20 amp breakers. ( It only had a single 10 amp before. ) Thanks for the help. Scheduled inspection mid week.