Ground Wire Behind Receptacle Box

Hi guys,

I have a house that was built in the mid 60's. The house has 3-wire Romex, but for every single receptacle box in the house, the ground wires are tucked back behind the metal receptacle boxes. I am replacing the two-prong outlets with 3s, but I need to ground them and am not sure how to do it correctly. Can I run a ground wire from the outlet to the back of each box? Or do I need to cut out each of the boxes to get to the ground wire and then replace each of the boxes with cut-ins?

Thanks...
 
  #2  
Old 04-07-13, 08:36 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
From the box is fine once you have verified with a multimeter you have ~120 volts from hot to the metal box.
 
 