220 circuit breaker problem
#1
Member
Thread Starter
Join Date: Apr 2013
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
220 circuit breaker problem
all of my 220 appliances quit working. The normal outlets and light switches work still. I tried replacing my 100amp and that didn't take care of it. What could the problem be?

#2
What 100 amp? Your first overcurrent protection device or a breaker supplying a subpanel. What voltage do you get when you measure between the hots at the main breaker? Be very careful when measuring between the hots.
#3
Welcome to the forums.
If your 240v appliances stopped working that would suggest that you lost one of your hot legs. There are two hot legs required for 240v appliances.
If you have lost one leg then every other breaker in your panel should be dead which means you should have lost at least some of your 120v circuits.
You're going to need a voltmeter to check for the 240 VAC in to your panel. You'll need to identify the incoming service wires to the main breaker and check there to see if you have an issue before the main breaker.
If your 240v appliances stopped working that would suggest that you lost one of your hot legs. There are two hot legs required for 240v appliances.
If you have lost one leg then every other breaker in your panel should be dead which means you should have lost at least some of your 120v circuits.
You're going to need a voltmeter to check for the 240 VAC in to your panel. You'll need to identify the incoming service wires to the main breaker and check there to see if you have an issue before the main breaker.
#5
Member
Thread Starter
Join Date: Apr 2013
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
it starts out at a 200 amp panel and and divides from there into two100 amps, one to a trailor and another to a building out back. inside each of them there is a 100 amp panel box
#6
Ok..... so at the 200 amp main panel check for 240 VAC on the 100 amp sub panel breakers.
Basically.... you need to verify 240 VAC coming in from the street. If you have that then you keep checking downstream. If you don't have 240 VAC from the street then you'll probably need to call the power company.
Basically.... you need to verify 240 VAC coming in from the street. If you have that then you keep checking downstream. If you don't have 240 VAC from the street then you'll probably need to call the power company.