Short circuit in 12/2 wire

Reply

  #1  
Old 04-24-13, 07:56 PM
Member
Thread Starter
Join Date: Apr 2013
Location: usa
Posts: 1
Short circuit in 12/2 wire

I have a dead short in a 12/2 romex cable buried under ground. I have been able to isolate the affected cable. Can I measure the resistance in the wire to calculate where the short is. What I mean is once I measure the resistance can I measure off in feet to where the short is.
 
Sponsored Links
  #2  
Old 04-24-13, 08:01 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,643
I have moved your post to its own thread. You had posted to someone else's thread and that can cause confusion.

No, a resistance reading won't help. Is this UF cable or NM-b (Romex) cable?
 
  #3  
Old 04-24-13, 08:56 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
No, but why do you want to know that? Don't you just need to replace the full run?
 
  #4  
Old 04-25-13, 04:46 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,354
If this is UF cable an underground splice kit can be used. If it is NM cable the entire run needs to be replaced.
 
  #5  
Old 04-25-13, 12:06 PM
Member
Join Date: Sep 2009
Location: USA
Posts: 484
You can't measure it with a multimeter but this could be done with a time domain reflectometer. Some electricians may have one. It will find the break. If this is a short run I'd just replace it.
 