New Bathroom Circuit

I am installing a new circuit in a bathroom for a floor and towel warmer. The two warmers draw less than 8 amps combined.

Should I use a 1 - 15 amp breaker (GFCI/AFCI) for both warmers with #12 or #14 wire?
 
Sponsored Links
  #2  
Old 05-11-13, 04:49 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 11,979
Any receptacle in a bathroom is required to have GFCI protection.

Any electric in-floor heat is also required to have GFCI protection.

15 amp breakers require #14 wire. 20 amp breakers require #12 wire.
 
  #3  
Old 05-11-13, 06:00 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,354
Are both the towel warmer and the floor heat 120 or 240 volt?
 
  #4  
Old 05-11-13, 07:03 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,212
What.......No heated toilet seat??
 
  #5  
Old 05-25-13, 06:41 PM
Member
Thread Starter
Join Date: Jul 2003
Location: USA
Posts: 31
The towel warmer and floor heater are both 120 volt!
 
  #6  
Old 05-25-13, 07:22 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
One 120V 15A circuit for both. GFCI circuit breaker. AFCI is not required on this circuit. 14 AWG wire (14-2/G cable).
 
  #7  
Old 05-26-13, 09:57 AM
Member
Thread Starter
Join Date: Jul 2003
Location: USA
Posts: 31
Thanks! Is it still okay to create 2 seperate 15A circuits from a 14-3/G cable?
 
  #8  
Old 05-26-13, 10:06 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 11,979
Yes. Be sure to use a two pole 15 amp breaker.
 
  #9  
Old 05-26-13, 02:21 PM
Member
Thread Starter
Join Date: Jul 2003
Location: USA
Posts: 31
Thanks for your help and advice!
 
  #10  
Old 05-26-13, 08:20 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
Is it still okay to create 2 seperate 15A circuits from a 14-3/G cable?
If your question is "Is it still okay to use 14-2/G cable to run a multiwire branch circuit with two hot wires that share a neutral?", then yes, it is. The better practice is to use two adjacent single-pole breakers to protect the two circuits and join the breaker handles with a handle tie, rather than using a 2-pole breaker. Using two breakers and a handle tie allows each circuit to trip on its own while still requiring that both will be turned off for servicing.

Is this question related to this project or a different one? Earlier you said
I am installing a new circuit in a bathroom for a floor and towel warmer. The two warmers draw less than 8 amps combined.
and I replied
Originally Posted by Nashkat1
One 120V 15A circuit for both.
Is there something I misunderstood?
 
  #11  
Old 05-27-13, 03:30 AM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,968
Check your controls for these two items. I just installed floor heating and it came with a built in GFCI, so none was needed at the panel. You don't want two GFCI's in the same mix.
 