Questions on 3 way switch wiring and others
Received 0 Votes
Hi,
Need some help wiring my basement.
Basically installing some pot lights in 3 sections all on separate breakers:
Section 1 & Section 3: 4 lights each w/ a dimmer. No issues.
Section 2: 12 lights w/ 2 dimmers on separate walls.
I have narrowed it to 2 options.
Option 1: Lights Between Two Three-Way Switches: Power Through Switch.
Option 2: End-Wired Switches: Power Through Light.
Question: When connecting the lights do I need to use 14/3 wire when looping light to light or just 14/2 between the lights and 14/3 to the switches?
Any help is much appreciated.
Welcome to the forums!
First of all, where are you? This is essentially a North American forum and it helps us focus our answers if we know where you're doing the work.
That said,
Choose Option 2. Bring the power into one switch box and feed the lights from the other. This will give you a neutral in each switch box, which is needed for many advanced controls.
Assuming a 120V 15A circuit, run 14-2/G from the panel to the first box, from the second box to the lights, and between the lights. Run 14-3/G between the switches.
Connect the black in the 14-2/G cable to the common, or point, terminal on each switch. Splice the neutral through with the white wires. Connect the black and red in the 14-3/G cable to the traveler terminals on each switch.
Connect color-to-color at each light.
That said,
I got those options from another website (see attachment) but they did not have a connection between the switches.
Besides being hard to follow and confusing, that diagram contains a number of actions that do not comply fully with either code or best practice.
Can you wire your system the way I suggested earlier?
Received 0 Votes
Thanks guys. This is all new to me (first timer doing wiring) and not an electrician. I can follow the diagram I posted but PJMax's diagram is a bit confusing to me. I am a bit dense when it comes to electricity mostly due to fear.
Nashkat1 Can you clarify your comment "Connect the black in the 14-2/G cable to the common, or point, terminal on each switch. Splice the neutral through with the white wires. Connect the black and red in the 14-3/G cable to the traveler terminals on each switch."
Some of the terminology means nothing to me in this context. "Common" or "point" "Splice the neutral through with the white wires"? What does that mean? Can someone clarify?
Received 0 Votes
This image shows the common terminal
[ATTACH=CONFIG]12756[/ATTACH]
Since a 3-way switch is a single-pole, dual throw, the common switches between T1 and T1. More-accurately, the common is tied to either T1 or T2, based on the position of the switch lever.
White is your neutral, and since you're just passing it through the boxes (neutrals don't connect to the switches), on its way to the light, simply tie all neutrals in each switch box together with a wire nut.
"Common" or "point"
Draw a "V". Make one side solid and the other dashed or open. That'e the schematic of a single-pole double-throw, or 3-way, switch. The point of the "V" is the common or "point" terminal. The other two points are the traveler terminals.
If you look carefully at Seattle2k's illustration and at your two switches, you should notice that one of the terminal screws is black and the other two are brass. The black screw identifies the common terminal.
Have you made an electrical splice before?
Received 0 Votes
Thanks guys for all the help. will read some more.
Nashkat1, no I have never made an electric splice before. When you say push it to the back of the box, I assume you mean tape & tie them together and tuck it in. What is the purpose of it? Thanks.
Use a pair of cable strippers to strip about 5/8" of insulation off the end of each wire going in the splice. Hold the wires together so that the ends of the insulation are even with each other. Use lineman's pliers to twist the wires together, with at least 3 good twists. Use the pliers to trim the ends of the conductors if they need it. By hand, twist on an appropriate-sized wire nut, clockwise.
Here's the longer version for the project you're doing: Use a pair of cable strippers to strip about 12" of the jacket of a 14-2/G cable; Use a utility knife to carefully cut the jacket of a 14-3/G cable. Feed the cables into the box until the jacket appears inside. Clamp the cables if you're using metal boxes.
Make up the grounds first. If you're using metal boxes, start a ground screw in one of the holes in the back. Loop and crimp the ground conductor from the cable bring power in around the ground screw, and tighten it. Trim the other ground conductor(s) back to leave about 3" in front of the box. Push the shorter ground conductors into the box so that they touch the ground screw and lie next to the long ground wire. Trim, curl and connect the long ground wire to the device.
Do the neutrals next. Trim and splice them as above. If your device needs a neutral, cut a 6" to 8" white pigtail and add that to the splice. Once you have made the splice, fold the neutrals into the back of the box with the wire nut pointing up. Connect the pigtail to the device if needed.
If unswitched power is going beyond the box, splice the power wires with a pigtail as above and connect the pigtail to the device. This won't apply to what you're doing. Just strip, curl, crimp and tighten the power conductor to terminate it to the common terminal. In one of the boxes, the power conductor will be bringing unswitched power from the panel. In the other box it will be taking switched power to the lights.
Note:
Or you can break this section in two and control each of those separately.